Soft-starter for AC motors

Soft-starter for AC motors

Soft-starter for AC motors

(OP)
Hello,

I was wondering what is the behaviour of an ac motor soft-starter (variable frequency) in regards of:
-Short circuits
-Power factor


Thanks.

RE: Soft-starter for AC motors

Soft starters are not variable frequency.  Do you mean a VFD used as a soft starter?

Keith Cress
kcress - http://www.flaminsystems.com

RE: Soft-starter for AC motors

For the items you list, a soft-starter is very similar to a full-voltage starter.

 

RE: Soft-starter for AC motors

First get the correct usage of your terms, then we can discuss the issue. The differences between soft starters and VFDs make a a big difference in those two issues.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: Soft-starter for AC motors

(OP)
Sorry,

I meant a VFD used as soft-starter. I would like to know what happens with power factor and above all with short-circuit. I know that a directly connected ac motor contributes to short-circuits and I wanted to know what happens with VFD connected ac motors.


Thanks.

RE: Soft-starter for AC motors

Probably the VFD will issue alarms like f.e. short circuit or thermal overload ( i2t ) in the case of fault on the VFD output.

I do not get exactly what do you mean by PFC and VFD relation. Typically the PFC is done by external capacitor bank, and VFD used for AC motors can provide mostly only the break resistor connection and class I or class II EMC filter but not the power factor correction. But maybe I am wrong it is some time since I have solved VFD issues.    

RE: Soft-starter for AC motors

The VFD will present a good displacement power factor (typically .95) to the line, but there is a variable amount of distortion power factor to contend with depending on load. You can get VFDs with 18 pulse and/or what are called "active front ends" which can present cleaner power and better distortion pf to the line.

As far as short circuit contribution, it depends on the VFD topology. I'm not sure if there is any "official" determination as to whether a motor can theoretically contribute through a 6 pulse inverter, but technically no, it does not. Any energy left on the motor during a fault somewhere else would be blocked by the rectifier from contributing to the fault. But if you consider the very remote possibility of a complete short of the drive's power structure, i.e. line to load, then it is theoretically possible. Also, "regenerative" drives, i.e. those which pump motor energy back into the line for braking purposes, or the aforementioned active front end drives, are capable of putting energy back on the system.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: Soft-starter for AC motors

But if there are bypass contactors, very common with conventional soft starts and more common in the earlier days of VFDs, the motor will contribute to the fault if the bypass is closed.

RE: Soft-starter for AC motors

Good point. Especially if a VFD is used just as a soft starter, it's likely that it is bypassed when at full speed.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources