ACI 530-05 Slender walls, h/t

ACI 530-05 Slender walls, h/t

ACI 530-05 Slender walls, h/t

(OP)
What is the limit for a slender masonry wall, ratio h/t.  ACI 530-05 Section 3.3.5.4 refers the slenderness ratio exceeding 30, but I do not see where that code defines the ratio or the limit for a wall being slender.  I also looked in IBC.

RE: ACI 530-05 Slender walls, h/t

Unless they have recently added it, ACI 530 does not have a slender wall method for wall design like UBC had.  

RE: ACI 530-05 Slender walls, h/t

(OP)
Yes, I am just trying to find how to determine when a wall is considered slender, at what h/t ratio.  Does the code not specify this.

RE: ACI 530-05 Slender walls, h/t

ACI 530 does not directly specify this, which makes sense since it does not give a different procedure for slender walls.


 

RE: ACI 530-05 Slender walls, h/t

The higher slenderness is addressed implicitly by the section you referenced.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources