Substation GPR Drop-off Gradient Protection

Substation GPR Drop-off Gradient Protection

Substation GPR Drop-off Gradient Protection

(OP)
When we examine the GPR gradient at a substation, there is a very steep drop-off at the edge of the grid.  Has anyone protected people against this steep gradient by using commercially available insulation such as using rubberized "nugget chips" or a rubber sidewalk?  Extending horizontal grounding conductors beyond the existing grid simply extends the drop-off edge for the GPR, doesn't it?   

RE: Substation GPR Drop-off Gradient Protection

The potential drop from the Substation Ground Grid fence –if the grounding grid is extended 3ft outside – will be equal with Touch Potential.
The Earth Voltage at any point (x) outside the Grounding System can be evaluated using the expression:
Vex=2*Vg/PI*arcSin(r/(r+dx) where Vg is GPR ;r=equivalent radius of the grounding grid area; dx =distance from the Grounding Grid.
So, for a further 3 feet from the fence the potential drop will be less than Step Potential and from here the potential drop for each 3 ft will drop dramatically.
As example, for 10000 sq.ft area and 3 KV GPR the first potential drop up to 6 ft from the fence will be approximately 600 V, further 240 V and so on.
My opinion is you don't need isolation unless pipes or rails enter the Substation perimeter.
Regards
 

RE: Substation GPR Drop-off Gradient Protection

GPR is the grid voltage with respect to remote earth.  It is a single value.  I think what you are referring to is the surface voltage gradient.  The gradient in V/m is the same as the step-voltage.  

As Zanoter indicates, this is normally not a problem unless you have pipes or rails that locally distort the gradient or if there is something grounded within reach (making the step-voltage into a touch-voltage).  The step-voltage along the perimeter does need to be checked, however, and if necessary, an insulating surface covering like crushed rock can be extended beyond the grid area.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources