Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Donate Today!

Do you enjoy these
technical forums?
Donate Today! Click Here

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

HVAC design for high altitude with standard psych chart

aumechengr (Mechanical)
3 Sep 08 17:02
Hello,

I am trying to determine how to use the standard psych chart in calculating the sensible and latent loads for a space. It is located in Salt Lake City, UT and will be a once through system.

I know that there will be a factor applied for the difference in air density ratios. If so I am assuming you read the numbers from the chart as if you were at standard conditions and apply it only to the following equations:

RSH = 1.08*Factor*CFM*Delta T
RLH = .68*Factor*CFM*Humidity Ratio

I would appreciate a little help with this.

Thanks in advance,

aumechengr

MintJulep (Mechanical)
3 Sep 08 17:20
Easier yet, there are many freeware psychrometric property programs, most of which allow you to specify elevation.
RossABQ (Mechanical)
4 Sep 08 9:14
Prior to availability of computerized selection programs, many fan and coil vendors used to select for sea level and try to correct the result to altitude.  For processes involving dehumidification or humidification, (not pure sensible) the results were not always accurate.  ASHRAE, Trane, and Carrier all have psych charts for 2500 and 5000 ft, I would use them from the get-go.  For sensible work at 5000' the first equation is approx. 0.90 x cfm x dT.

In the '90's I found many installations with incorrectly sized fan motors and coils from the old approach used in the '70's.  
quark (Mechanical)
5 Sep 08 4:09
ASHRAE HOF suggsts the following equations.

SH = 1.1 x cfm x dT
LH = 4840 x cfm x dW

Now the correction for altitude is the constant x (P1/Pa)
(Page 30.13)

P1/Pa can be calculated as (1-((6.8754x10^-6)*Z))^5.2559
Z is altitude in ft.

This correction is only for altitude. If you use the sensible heat corresponding to the temperature, you can have precise factors.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close