Latent cooling (Moisture Cooling)

Latent cooling (Moisture Cooling)

Latent cooling (Moisture Cooling)

(OP)
I know I can calculate sensible cooling energy with the equation KW=(1.08*CFM*delta_T)/3412 (BTU/KW).  How do I calculate energy for latent cooling?  

RE: Latent cooling (Moisture Cooling)

Qt = m.dh
Read h from your Psych chart at each state point and use mass of air.  This is the total heat; latent + sensible.  You can easily calculate the sensible and subtract, or use the slope of the line to determine the sensible heat ratio from the protractor tool usually printed on the chart.

In water terms, you are adding or removing moisture by evaporation or condensation. So optionally, you can determine the total moisture removed from the absolute humidity scale and use:
Ql = hfg.dW
The heat transfer is 2465kJ/kg or 1060 BTU/lb x the mass of water removed.   

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources