Reversed Polarity on Closed Delta Bank
(OP)
What effects will reverse polarity have on a closed delta bank? Will the adverse effects on equipment be instantaneous or over a period of time?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Reversed Polarity on Closed Delta Bank
|
RE: Reversed Polarity on Closed Delta Bank
Keith Cress
kcress - http://www.flaminsystems.com
RE: Reversed Polarity on Closed Delta Bank
Do you mean reversed polarity of one transformer in the bank?
Very heavy secondary circulating currents and primary currents. Expect the transformer primary fuses to blow and possibly the distribution feeder to trip out. Possible transformer damage.
Negligible effect on the loads.
Bill
--------------------
"Why not the best?"