Can anyone help me understand the difference between types A, B, C, D etc MCCB/MCB? Reference to the relevant EN would be useful.
Thanks
Thanks
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: MCCB Types
I think you are refering to tripping curves. Standard is BS EN 60898, it think I don't have books at home to check and the memory is not what it was.
A breaker with a B curve has a magnetic trip 3 to 5 times Rated current (In) and is typically used in domestic type installations
Type C mag trip is 5 to 10 times In.
Type D mag tip 10 to 14 times In.
To select the correct breaker you need to know the inrush when the load is energised. Typicaly a motor will be 6 times Full load current.
You also get catorgory A & B breakers, this is defined in BS EN60947-2 and refers to tripping delay provided. This nornally refers to Moulded case circuit breakers (MCCB) rather than MCB.
Hope this helps