Hi guys
I have an Omron relay part# G5V-1-DC24 with contact rating:
            1A at 24 VDC
    or      0.5A at 115VAC
I want to use it for 12VDC ,is the rating of the contacts remain at 1A or could be more than that?
Thanks      

RE: Relay question

The relatively small difference between 12 and 24 volts would probably have a negligible impact on the current rating. So it's best to assume the contact rating remains at 1A.

The type of load has impact on contact life as well.

 

RE: Relay question

I would take the ratings as maximums;
On DC, the maximum current is 1 amp and the maximum voltage is 24 volts.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Relay question

(OP)
Thanks for help.
Also, I would like to know why that differences between AC and Dc ratings ?
If I use it for 24VAC is the current rating remain at 1A?

RE: Relay question

I don't have an Omron catalog but I would be comfortable running it as a 1 amp rated relay (with your standard safety factor built in). Somewhere in the catalog should be a section on interpolating the printed ratings to match their design standards.

Luck is a difficult thing to verify and therefore should be tested often. - Me

RE: Relay question

Mackmaster,

The difference between AC and DC voltage ratings applies for most relays, and is higher for AC. This is because on AC any tendency for the contacts to arc on opening tends to be quenched when the voltage changes polarity on the next half cycle. With DC, an arc, once started, will tend to persist, so keeping the maximum voltage rating lower helps avoid this problem.  

RE: Relay question

The "carry" current means the maximum current that the contacts can handle once they have completely closed. This is different to the maximum current (AC OR DC) as this is the current permitted that the contacts can SWITCH (either closing or opening)without damaging the contacts.  

RE: Relay question

Good design practice would be to use the values in the graphs under "Characteristic Data" as maximums. Exceeding these values will probably result in shortened life of the device and may lead to problems interrupting currents greater than rated currents. I would forget about the "Carry Current". It is not usually practical to use in designs. It is dangerous to use a relay or contactor to carry more current than it can safely interrupt.  

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources