paint spec
paint spec
paint spec
what is the best type of paint for use outside in an area close to the coast?
RE: paint spec
Best coating--hot dipped galvanizing
Next best--inorganic zinc over white metal
RE: paint spec
You asked the $64,000,000 question. I have to evaluate coating proposed for US Navy equipment all the time and I found this table a few years ago that I just love.  It rates paint coatings on steel based on the surface preparation, environment and service life.  I use it to specify performance with statements like: "Coatings shall have a minimum expected life of 15 years in a Seacoast Marine Heavy Industrial envioronment when rated per NACE paper No. 477 or similar nationally recognized rating system".  This reference is a more concise table printed by a paint manufacturer.  I have printed out the actual report but I couldn't find the web reference right off.  It is from the 1996 Inernational Corrosion Conference.
http://ppgamercoatus.ppgpmc.com/psxTechnology/pdf/NACE_477A.pdf
RE: paint spec
Interesting table, RockEngineer.  Intriguing that no ratings are shown for galvanising, either as a stand alone coat or as the first of a system.  Since it was produced by a paint manufacturer, I guess that explains it.
RE: paint spec
In a marine environment, that is.