(OP)
It seems like every software I use has different entry parameters for three-winding transformers.  I think I have an analysis setup correctly in SKM PowerTools for the following three-winding transformer, but wanted to check to make sure:

Primary: Wye-Grounded
Nominal KVA: 25000
Rated Voltage: 34400

Secondary: Wye-Grounded
Nominal KVA: 25000
Rated Voltage: 17200

Tertiary: Delta
Nominal KVA: 3750
Rated Voltage: 2400

I have entered the following Positive Sequence Impedance:

Primary-Secondary = 0.34 (%Rpos), 7.8 (%Xpos)
Primary-Tertiary = 1.24 (%Rpos), 28.46 (%Xpos)
Secondary-Tertiary = 0.81 (%Rpos), 18.59 (%Xpos)

My specific question involves the entry of the Zero Sequence Impedance data.  I checked the Westinghouse T&D Book and it states that the Zero Sequence Impedance is equal to the Positive Sequence Impedance for this 3-winding transformer configuration.  Thus, in SKM PowerTools do I simply enter the same impedance information from the positive sequence for the below zero sequence values?

Primary-Secondary = (%Rzero), (%Xzero)
Primary-Tertiary = (%Rzero), (%Xzero)
Secondary-Tertiary = (%Rzero), (%Xzero)

Thanks in advance.

 

RE: Three-Winding Transformer / SKM PowerTools Representation

First you have to know shell or core type construction.  For shell construction Z0=Z1, also applies to a bank of three single phase transformers.  For core type construction Conrad St. Pierre suggests that:
Z0H-L=0.85*Z1H-L
Z0H-T=0.75*Z1H-T
Z0L-T=0.9*Z1L-T

Based on real world fault data I would suggest that St. Pierre may be on to something.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources