Opening allowed in Segmented shear wall?

Opening allowed in Segmented shear wall?

Opening allowed in Segmented shear wall?

(OP)
For a standard segmented wood framed shearwall, is there a maximum opening size allowed prior to analyzing it as a shearwall designed for force transfer around openings. I have a 12" exhauset pipe from a propane fireplace exiting through my 4' shearwall. The building department is requiring a perforated shear wall calculation. This doesn't seem very practical.

RE: Opening allowed in Segmented shear wall?

IBC/IRC2006 has some examples.  Maybe that will help.  

Good golly - these guys are getting more and more picky - but I send them Xmas cards every year because I get more business every year!!!!!

RE: Opening allowed in Segmented shear wall?

(OP)
I understand how to perform the analysis for perforated and how to transfer forces around and opening. My question is at what opeining size is this required? Or is in any opening?  

RE: Opening allowed in Segmented shear wall?

I don't know - but if the building official is asking for it - then it is too big...

They call the shots and the code says they can.  Good luck.

RE: Opening allowed in Segmented shear wall?

Effectively, the force per foot in your wall is increased  locally by 33% locally at the opening.  This is not small.  I can see that some special reinforcing, increased nailing would be needed in the region.  No additional holddowns though.  A perforated analysis would be conservative here.  

If the wall was 10 feet long, I would argue the point, but not at 4 feet.

Mike McCann
MMC Engineering

RE: Opening allowed in Segmented shear wall?

(OP)
Thank you all.

RE: Opening allowed in Segmented shear wall?

If you look at your Co factor (table 2305.3.7.2 in the 03 IBC) you can have a factor of 1.0.  In other words openings that are small enough don't change the capacity of the wall.  look at that and see if your "piers" still meet the code provisions.  Sounds like a case of educating the code official to me.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources