Protection System DC Bank Grounding

Protection System DC Bank Grounding

Protection System DC Bank Grounding

(OP)
I am putting together the DC system for a power plant protection system. For the floating DC system, looking for any pro's or con's for fusing both the DC positive and negative inputs of the protection relays or only needing to fuse one side.

Is there any standards with respect to fusing for the protection's DC system.

thanks for any replies in advance.

RP

RE: Protection System DC Bank Grounding

ONLY BOTH.
Regards.
Slava

RE: Protection System DC Bank Grounding

+1 for fusing BOTH sides.  

RE: Protection System DC Bank Grounding

Another for BOTH.

RE: Protection System DC Bank Grounding

Agree with both. The single line to ground fault causes no trip and no overload. The second ground fault of the opposite polarity causes the trip. But what if the two faults are on the opposite polarities of separate and unequally sized circuits? The smaller unprotected wire of one circuit will burn waiting for the longer time of the second circuit's fuse to clear.

Not a standard, but a good IEEE PRC reference is at http://www.pes-psrc.org/k/rlytrckt.zip

RE: Protection System DC Bank Grounding

(OP)
Thanks to all:)

RP

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources