ACI:What are the factor of load cases in analysis of piles
Hi All,
I am working in project designed by ACI.
With members of the body structural part( slab, beam, column) I used combination with factored load (these combination are shown detailly in ACI).
to calculate the numbers of pile, I want to use allowable stress design (in which Force at top of pile compared with allowable capacity of pile), and use combination with unfactored loads. But I can not find provision showing detailly about these combination in ACI.
Could you kindly please give me a detail table about these above combination, for example:
1. f1D+f2L;
2. f3D+f4L+f5W;
3. f6D+f7L+f8E;
with f1=; f2 = ...
I am looking forward to hearing from you
1. f1D+f2L;
2. f3D+f4L+f5W;
3. f6D+f7L+f8E;
with f1=; f2 = ...
RE: ACI:What are the factor of load cases in analysis of piles
D + 0.75L + 0.75W
0.6D + W
D + 0.75L + 0.75(0.7E)
0.6D + 0.7E
With these load combinations, a 1/3 increase in allowable capacity is not permitted.
DaveAtkins
Your counsel are highly appreciated.
One more question:
I found in IBC that "when having more than two or more transient load act simultaneously with the dead load,IBC 1605.3.1.1 permit a 25% transient load reduction-> have factor = 0.75 in these cases. And I found the same in ACI standard;
But: About a 40% reduction of dead load in combination (0.6D+W, 0.6D+0.7E), I only found in IBC, did not in ACI;
Could you kindly show me:Where in ACI say about this reduction or where in ACI permit use IBC code (because in my project I have to use ACI code)
I look forward to hearing from you
Chapter 8 (of ACI318-08), Section 8.2, defaults to ASCE 7. Chapter 2 of ASCE7,"Combinations of Loads" calls out the Basic Combinations in 2.3.2. IBC Section 1605.3 is similar to ASCE7.
I hope that this answers your question.
In the two cases you asked about the 0.6D does not represent a 40% reduction in dead load. Rather it is a 40% reduction in the stabilising effect of the dead load against the wind or earthquake load. In other words, watch the signs.
DaveAtkins
Thanks for your answers. They make me understand clearly about load combination.
I wish that we can discuss more in future.
With very best wishes,
OSE