Working on a project were the utility company has requested a grounding bank be connected to the primary of their 12KV delta-wye transformer used as a generator step up for (3) 480V landfill gas generators. It will be located outdoors on a pad with the utility transformer and wired to the generator protection equipment. Can anyone reccomend a manufacturer who makes this type of equipment. Is grounding bank the correct terminology? Google searches come up empty.






RE: MV Grounding Bank?
Historically, this has been done using zig-zag grounding transformer, but can also be done with a small wye-delta transformer.
Google up "grounding transformer" and see what turns up.
RE: MV Grounding Bank?
You say on primary of stepup trafo, that makes it 480V terminals of the trafo. Generator step-up transformers have delta on generator side (generally speaking) and that makes it on 480V side in your case.
If so, where is the need for artificial grounding - 12kV is Star with neutral point available and on 480V side, generator star point can provide grounding!!
May be you would like to clarify.
RE: MV Grounding Bank?
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MV Grounding Bank?
RE: MV Grounding Bank?
RE: MV Grounding Bank?
I suspect that the OP is looking for a high resistance/impedance neutral grounding device. I suspect that the transformer is 480 V delta and 12kV wye. In this case do we have to be concerned with high side ground fault current through the transformer? The GSU may be existing and just need a grounding resistor.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MV Grounding Bank?
A far better solution would be to connect the generators to their own transformers, Δ on the generator side and grounded wye on the 12kV side. Now they're not looking at a grounding transformer that is unneeded almost all the time. But when it is needed it better be there or there will be all sorts of trouble.
RE: MV Grounding Bank?
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MV Grounding Bank?
Can you explain the situation in your last post further. Do you mean between the time when the utility breaker opens and the generators are connected to the system. With utility and generators wouldn't one be closing as the other opened?
RE: MV Grounding Bank?
RE: MV Grounding Bank?
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MV Grounding Bank?
RE: MV Grounding Bank?
Could somebody please post a single line for this arrangment. I think I am understanding everything but having a hard time visualizing it.
RE: MV Grounding Bank?
RE: MV Grounding Bank?
How big are your generators?
Is it necessary to parallel the generators with the grid?
If the generators are small compared to the 12kV source MVA of the utility, the, You should be able to convince the utility that the contribution (for 12kV system earth faults) from the generators is not much and seek waiver from the requirement of providing grounding trafo at 12kV.
RE: MV Grounding Bank?
Without the grounding transformers the fault contribution by the generators, no matter the size, will be approximately zero and that is the problem. The grounding bank is necessary so that there will be ground fault current and the voltage will be stabilized.
RE: MV Grounding Bank?
I agree with you that the ground fault contribution is zero. With grounding transformer, the contribution from generators to the ground faults in the utility power system can be ensured. That is one part.
I am looking at a case when the utility fault level is large enough even without considering the contribution from these generators. If true, this would save the bother of retrofitting the grounding transformer.
The over voltages in 12kV system is not an issue here, I hope. The utility system must have 12kV neutral grounded at the source end.
Hope I could clarify.
RE: MV Grounding Bank?
The problem arises after the utility feeder breaker opens on a ground fault and the feeder is still supplied by the generator.
With no generator ground, the generator will not contribute to a ground fault and will not trip on a feeder ground fault.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MV Grounding Bank?
The whole concern is during the few cycles between the utility substation breaker opening for a ground fault on the circuit and the generators separating from the circuit. Even with transfer trip the generators will be on the circuit for 1-2 cycles longer than the substation. That 1-2 cycles is long enough to do considerable damage.
We will never approve customer generation in parallel with a general use feeder circuit unless the generation always appears to be effectively grounded from the point of common coupling.
In the system of the OP, it would be much better for the generators to be behind a transformer that is grounded wye on the high side and delta (or even grounded wye) on the generator side.
I'd hate to have to make the economic justification for a grounding transformer that is only needed during fault conditions. But I will require that transformer without hesitation if that is the only way to ensure that the customer generation appears to be effectively grounded when seen from my circuit.
RE: MV Grounding Bank?
The utility is providing a 1500KVA 12KV delta to 480V Y pad mounted transformer. They are not interested in supplying a different type. There are 3 generators each rated at 480V 300KW. Attached is a cut sheet of what we found for the potential ground fault sensing equipment. They want the ground fault equipment pad mounted. Does any one have any suggestions for alternative ground fault sensing equipment. I have only found this one vendor and the lead time is to long. The other option is to mount the equipment on a pole but this may not meet their requirements as all other equipment is enclosed pad mounted type.
RE: MV Grounding Bank?
RE: MV Grounding Bank?
RE: MV Grounding Bank?
Avoid a grounded wye primary/delta secondary(480). This connection may overload your transformers and will back feed full voltage to a single open primary phase. (Subject to impedance drops).
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MV Grounding Bank?
The generators are located at a muncipal landfil. The utility company is providing a 1500KVA, 12Kv to 480V transformer delta primary (12Kv) wye secondary (480V) There is no negotiation this is what they are providing. Utility will be buying the power from the company that is installing the generators and gas equipment at the site. The utility company requires a ground fault sensing on the primary side to trip the generators and protect the grid. This is being done with a "grid protection package" which is a Beckwith relay provided by the microturbine vendor. The ground fault sensing will be done using three 12KV instrument class Pt's wired in a broken delta formation. The utility refers to this as a "ground bank". This equipment needs to be installed in a pad mount enclosure. It will be wired to the loop bushings on the main transformer. I have recieved a wealth of information but no one has adressed my main question. Can any one recomend a vendor who would build this enclosure and provide the PT's and other equipment in a package? The only one I have found thus far is Elliot Industries. Design is approved equipment is purchased. Only open item is the "ground bank". If any one can reccomend a vendor I would appreciate it.
Thanks,
jd
RE: MV Grounding Bank?
Not the way I'd require it done, but that isn't my system.
RE: MV Grounding Bank?
If so, should they be full 12kV line to line rated PTs with the secondaries at 69 volts?
I can't understand how a ground would be detected unless the primary has a ground reference.
If the PT wye point is grounded, then when one phase is grounded the voltage will rise to 12kV on the healthy phases and the secondary voltage will rise to 120 volts.
Although the normal voltage across the PTs will be 6928 V, with a grounded phase this will rise to 12 kV and would saturate and destroy 6928 V PTs.
.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MV Grounding Bank?
On a system that could become ungrounded, you are absolutely correct that the VT primary voltage needs to be the line-line voltage. This scheme has been regularly used on grounded systems as a polarizing source for directional relays and in that case the VTs can be line-neutral rated as the voltage shifts are not as severe - much more a loss of voltage on the faulted phase than a voltage rise on the unfaulted.
RE: MV Grounding Bank?
I'd start the mfg. list in the reverse of the order listed if time is the primary driver for the installation.
RE: MV Grounding Bank?
try not to get too stroppy about people not answering your question, when you yourself did not explain until your 5th post, what you actually wanted.
the line of thought that was explained throughout this thread was completely valid with the limited, if somewhat misleading information that you supplied.
in your first post you asked the question "grounding bank the correct terminology? Google searches come up empty.". Maybe this should have triggered you to explain up front what you wanted in a bit more detail.
It took 9 days to work out what you asked, and one day to answer the question. I think that the contributors deserve a little more than attitude mister "One Last time,"
ausphil
RE: MV Grounding Bank?
I am in the process of getting competetive quotes for a custom pad mounted unit. In addition to the quote from Elliot Industries, Maysteel and Power Design Inc. have previously built similar units and are quoting their solution.
Your help has been invaluable.