Grounding transformer to enclosure

Grounding transformer to enclosure

(OP)
A manufacturer of 345 kV circuit breaker provided a 7.5 kVA transformer 480-240/120V for with a neutral grounded on the control cabinet. This cabinet is bolted to the metallic part of the circuit breaker witch is grounded to the substation ground grid at the base.

The local utility engineer is challenging the transformer grounding to the enclosure instead a direct grounding conductor connected to the substation ground grid.

I have a hard time finding any code violation or no compliance to the NEC, IEEE,  NESC etc. regarding the grounding proposed by the manufacturer.

Please advise if there is any objectionable grounding in this arrangement.

Thanks
 

RE: Grounding transformer to enclosure

This material was extracted from Mike Holt Training Materials copyright 2007 by permission. Visit www.MikeHolt.com or call 1.888.NEC.CODE (632-2633) for more information.

RE: Grounding transformer to enclosure

(OP)
Thanks Zazmat

RE: Grounding transformer to enclosure

cuky,

I think the concern may be the reliability over time of using the enclosure as a ground path, especially on a high voltage breaker.  As corrosion sets in, the ground path through the bolts and metal-to-metal interfaces could increase in resistance.

I do not think it is an NEC issue, but just question of what is the "best practice".  



 

 

RE: Grounding transformer to enclosure

I assume that the transformer is for local auxiliary power purposes.  If this is the case, then no load or fault current on the secondary will flow through the ground grid anyway.  There is no question of reliability of the path to the ground grid since it will never carry any current.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources