Circuit Question
Circuit Question
(OP)
Hello,
We have a circuit which contains 5 flow switches in series(NC) which turns on one 120VAC relay. I have attached a diagram for what we currently have.
If anyone of the switches open, it turns on that light and the relay turns off, shutting the equpiemnt.
What we would like to do is add in 120VAC relays inplace of the light to give use more flexiblity. The problem is that we don't know how this will work in the circuit using the coil of the relay instead of the inductive light. The coils are 1.5K.
Thanks for any suggestions with this
We have a circuit which contains 5 flow switches in series(NC) which turns on one 120VAC relay. I have attached a diagram for what we currently have.
If anyone of the switches open, it turns on that light and the relay turns off, shutting the equpiemnt.
What we would like to do is add in 120VAC relays inplace of the light to give use more flexiblity. The problem is that we don't know how this will work in the circuit using the coil of the relay instead of the inductive light. The coils are 1.5K.
Thanks for any suggestions with this





RE: Circuit Question
For what you presently have the lamps have to light on enough less current that the relay can't remain pulled in. Going to relays it will probably be pretty hard to run other relays in lue of the existing one.
You could use Solid State Relays(SSR) instead of mechanical relays and that would work.
Do you have a specific relay you want to use? We also need the specification of the existing relay.
Keith Cress
kcress - http://www.flaminsystems.com
RE: Circuit Question
We don't have any specification on relays except for 120VAC coil. These are just standard relays SPDT.
Why would an SSR relay work but not the coil type.
Thanks
RE: Circuit Question
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: Circuit Question
Based on the circuit, is it the low current and impedance of the light that makes this work.
If so and if I can match the current and impedance of the light with a SSR I shouldn't have any problems?
The light is around 47K resistance.
Thanks
again
RE: Circuit Question
If you put an identical relay across one of the switches (Let's look at only one for now, it gets worse with more than one) When the switch opens, two identical relays will be in series.That means that each will get 50% voltage. depending on the drop out voltage of the relays, either both will drop out or both will hang in. Neither is the result that you want.
If you use the SSRs that itsmoked suggests, the high impedance of the SSRs will not pass enough current to hold in the relay.
You don't have to match the lamps impedance exactly, but you do need SSRs with an impedance that is high in relation to the electro mechanical relay.
itsmoked is more familiar than I with SSRs. Any advice he gives you should be good advice.
I think that Gunnar means that if the SSRs do pass enough current to operate the relay coil, a load in parallel with the relay coil will cure the problem.
Gunnar's advice is also usually very good.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Circuit Question
Why not wire up each flow switch in series only with it's own relay coil (or input) - and power.
Then you can wire up the relay contacts (or outputs) to do whatever you want; including making individual indicator lights work and tripping off the equipment. Especially easy if the relays contacts are DPDT.
The circuit would then become boringly bog-standard with zero trickery.
Downside is that you might need more wire.
RE: Circuit Question
Is this a one-off or a product you're talking about?
Keith Cress
kcress - http://www.flaminsystems.com
RE: Circuit Question
VE1BBL has the answer, you must have the wires already, for the lights.
If you have a PLC you could wire from each contact to a 120V input then use some logic to display just the first open.
Roy
RE: Circuit Question
This is one of the kind circuit.
We might look into placing a relay in series with each flow switch and use it's contact to series all them together.
RE: Circuit Question
Trying to put relays where you show lights in your drawing is just asking for problems.
RE: Circuit Question
I asked about quantity because SSRs bought in small quantiles are kinda pricey. If you were making a bunch of systems I'd have suggested soldering smaller thruhole pin based units into a circuit board as you could save $$, but for a one off, I'd just use the standard hockey puck units.
Keith Cress
kcress - http://www.flaminsystems.com
RE: Circuit Question
You may be able to get high voltage AC Input but they are not so common. The low voltage DC are a lot safer if you have that available.
Roy
RE: Circuit Question
Keith Cress
kcress - http://www.flaminsystems.com
RE: Circuit Question
The last thing you need is someone replacing a failed relay in the future with one that doesn't work just because you had to get "smart" with your wiring technique. Basically not understanding the circuit and why it was done that way and then finding a way to screw up the protection.
If you were designing a circuit board for this function then you could get fancy since no-one else would likely be modifying it down to the board level. But, with point-to-point control wiring it's not worth trying, especially when wiring it the more normal expected way really does not add anything extra to the circuit except some more wire.