AC Hi-pot Sizing

AC Hi-pot Sizing

AC Hi-pot Sizing

(OP)
I am looking to conduct an offline partial dischrge test on a synchronous generator.  I need an AC Hi-Pot machine with a rating high enough to overcome the winding impedance and  bring each phase winding up to phase voltage (10.4 kV).  Can anybody tell me how to properly calculate the required output rating for the AC Hi-Pot machine to conduct the test? I had one rated for 3 amps, but it would blow its output fuses before the winding got to full voltage.

RE: AC Hi-pot Sizing

Here is a tip, get a VLF hipot and save the trouble and thousands of dollars.  

RE: AC Hi-pot Sizing

Since you say phase voltage is 10.4 KV, I assume it is a big machine (over 200 MW ?) For such machines, the winding capacitance would be around 0.25 to 0.35 microfarad. I am sure you can do the math to get the current.

RE: AC Hi-pot Sizing

In the US contact Advanced Testing Systems at www.advtest.com they have a number of trailer mounted series resonant test sets designed for generator testing.

RE: AC Hi-pot Sizing

phoenix also makes big units.

I've heard that VLF can be used, but has some other issues, depending on the PD sensing technology and means of coupling.

RE: AC Hi-pot Sizing

No problem with VLF at all and if you do the math for the size of the power supply needed at 0.1Hz compared to 60Hz you will see the advantages of VLF.  

RE: AC Hi-pot Sizing

The only trouble with VLF is that the PD results can not be compared to IEEE standards. You need power frequency to use the standards.

Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants

RE: AC Hi-pot Sizing

Thank you benlanz. I was waiting for someone better than me to say that. VLF is touted as an easy way out in many cases where power frequency plays a crucial part in the test results and interpretation.

RE: AC Hi-pot Sizing

If you have a large data base of PD samples and VLF frequencies I dont see what the problem is.  

RE: AC Hi-pot Sizing

ZogZog,

Do you know of anyone or any firm who has a database (of any size) of PD values associated with VLF testing of generators?

If you get a chance, please forward the info to me.

Thank you.

RE: AC Hi-pot Sizing

IQ systems in California

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources