(OP)
Hi,

i'd like to know

where should i install CT for REF, before (upstream) or after (downstream) 40 Ohm NGR on 150/20 kV 30 MVA Tx ?

thank you





 

RE: CT REF location

Do you want the NGR included in or excluded from the zone of the REF?

RE: CT REF location

If installed upstream, the CT installation may be subjected to 11,547 volts to ground in the event of a ground fault. Downstream of the resistor the voltage to ground will be zero volts.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: CT REF location

Hi.
Standard connection will be upstream ( before NGR) connection of CT.
Biil you are right, in case of "before" is HV type od CT, "after" is low voltage.
Regards.
Slava

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources