We are installing a small water treatment plant and contracted to have 220v single phase power supplied to the site. the contractor installed two wires(850'in length) to the panel with a ground rod connection to the breaker panel. He stated that he would install a transformer for any 110v requirements we had. The control panel (a duplex type for 2 220v single phase pumps which pulls power from one leg for the 110v analyzers, samplers etc.) requires a neutral for the 110v equipment. The electrician is now telling me that a transformer will not give me the neutral I need. I contacted the panel builder and one solution is to replace the 220v starters with higher amp 110v units. My basic question is; can I come up with the neutral I need without repulling the line wires & adding a neutral($3K) or purchasing new starters? Thanks for any advice.





RE: Transformer Query
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Transformer Query
Your control supply needs 110V between two supply wires, one of them does not have be a neutral per se. Any 220V:110V control transformer will have two terminals on the secondary side with 110V between them. Either one of them can be assigned as "neutral" if you want to call that.
RE: Transformer Query
Keith Cress
kcress - http://www.flaminsystems.com
RE: Transformer Query
RE: Transformer Query
RE: Transformer Query
I have used these with great success:
http://ww
Beware you generally need fuses on both sides. Some of these will have nice holders mounted on them.