Wet "Live" Tapping or Dry Tapping?
Wet "Live" Tapping or Dry Tapping?
(OP)
On a newly installed watermain in a subdivision (8") is it better to wet tap or dry tap the services onto the main?( right now the main has no water in it) and why?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Wet "Live" Tapping or Dry Tapping?
|
Wet "Live" Tapping or Dry Tapping?Wet "Live" Tapping or Dry Tapping?(OP)
On a newly installed watermain in a subdivision (8") is it better to wet tap or dry tap the services onto the main?( right now the main has no water in it) and why?
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: Wet "Live" Tapping or Dry Tapping?
RE: Wet "Live" Tapping or Dry Tapping?
The main is empty right now, would it be better to dry tap then charge the main, swab, pressure test, chlorinate and sample. Or charge the main, wet tap then swab etc.
i've always thought wet taping was better because it was easier to check for leaks on the main stop, check that the main stop was on (see water come out the curbstop) and it pushes the fillings out of the pipe.
Does anyone see it a different way?
RE: Wet "Live" Tapping or Dry Tapping?
Wet and Dry Taps
"Connections can be made either when the main is empty (dry tap) or whe the pipe is under pressure (wet tap). Dry taps are made only during the installation of a main. Most tapping done today, whether on a new or existing mains, is wet tapping. This method is preferred when adding a service connection to an existing main because it allows the connection to be made without turning off the water and interrupting service to existing customers. There is also less chance of contamination, since the pressure in the main tends to expel any foreign matter"
Intro to Water Distribution, AWWA 1986, vol 3, pp 94
RE: Wet "Live" Tapping or Dry Tapping?
RE: Wet "Live" Tapping or Dry Tapping?
On main line connections we almost always wet tap them.
RE: Wet "Live" Tapping or Dry Tapping?
Most then use wet taps.
The line item costs for wet or dry taps is the same.
If you do a wet tap, you will also be able to locate a leak at the time of the tap, rather than have to track down the problem later.
RE: Wet "Live" Tapping or Dry Tapping?
Also, e.g. if small taps and corp stops/service lines etc. are installed in the dry and prior to pressure tests, the pressure rating and capabilities of all elements/appurtenances then under pressure in the eventual test should probably be considered (I have heard that some modern mains and joints etc. are capable of, and now sometimes being subjected to, very high pressure acceptance tests, that can be well beyond e.g. the seat rating of at least some valves or corporation stops, etc.)
RE: Wet "Live" Tapping or Dry Tapping?
Shouldn't all elements/appurtenances of your water system be capable of handling the pressure that the system is normally operated at plus some factor of safety? Typical test pressures are 1-1/2 times normal operating pressure or 150 psi, whichever is greater. Unless you operate your distribution system at pressures above 130 psi, you shouldn't have any issues. You should take the pressure rating of all appurtenances into consideration if you require testing above 200 psi.
RE: Wet "Live" Tapping or Dry Tapping?
(25.4-mm) and smaller sizes, and 80 psig (560 kPa) for 11/4-in. (31.8-mm) through 2-in. (50.8-mm) sizes.
4.2.3 High pressure. High-pressure service line valves, fittings, service saddles, and meter setters shall be suitable for use with water at 100° F (38° C) and 150 psig
(1,050 kPa) pressure."
I guess if you are instead buying service valves that are good for 300 psi seat test/service, there would be no obvious problem testing against same, of course as long as the pressure was that much or less. You are of course correct one should take the pressure rating of all appurtenances into consideration, as "a chain is only as strong as its weakest link" (this is basically what I ws trying to say).