generator fault current
|
generator fault currentgenerator fault current(OP)
please let me know the fault current calculation of generator of 20 to 50 MW.
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: generator fault current
For the start:
I3ph-fault=Inom gen/X"d (for the turbogenerator from 13%-17%).
Regards.
Slava
RE: generator fault current
For 30MW 11KV Generator, rated current is 1968, Xd"(sat)-11.84% & Xd"(unsat)-14.79. i have to take saturation value or unsaturation value of Xd".
RE: generator fault current
You have use saturated transient X"d 11.84%
Regards and Good Luck.
Slava
RE: generator fault current
RE: generator fault current
you informed as below
For the start:
I3ph-fault=Inom gen/X"d (for the turbogenerator from 13%-17%).
but i have still one doubt i,e I nom gen (or) V nom gen.
RE: generator fault current
It is Inom in ampere and X"d in %
So I3ph = 1968/(11.84/100)