Cable Deration vs. 125%
Hi electrical folks. I am having a discussion with one of my colleagues regarding the cable sizing and we are on the matter of resolving some technical indifferences.
per NEC, it states that the conductors shall be sized not less than 125% of the full load current. In my way of sizing, I have maintained the 125% compliance. That means I will select a cable ampacity that is having an equivalent ampacity, after I multiply with a derating factor, higher than the 125% x FLA. Example, assuming I have FLA=30A, and my overall derating (temperature + grouping) = 0.50, my cable required ampacity is 30 x 1.25 = 37.5A, If I'm going to choose say #6 (with ampacity =65A) then applying 0.5 derating to it will result to 65 x 0.5 =32.5A which will be less than 37.5A or less than the 125% rule. Hence, a #4AWG (ampacity=85A) is selected which will give a derrated ampacity of 85 x 0.5 = 42.5A
On the other hand my colleague has another way,
Required ampacity = 30/0.5 = 60A, then with this, he may choose #6AWG which is 65A.
However, this will not satisfy the 125% rule since with this size, the cable is (60/65)x100%= 92% loaded or less than the 125% rule.
If I am not in violation of the code, then I would prefer the #6AWG which is costing less. But my question, is the 125% rule be maintained after conductor deration. What is the significance of this 125% rule for my understanding.
Thank you.
Thank you.
RE: Cable Deration vs. 125%
The (main) reason for the 125% requirement is that the circuit breaker that is used to protect the feeder is generally capable of carrying only 80% of its rating on a continuous basis. for example, a 100 A breaker can only carry a continuous load of 80 A. So for a continuous load of 100 A, the breaker rating must be 100/0.8 = 125 A = 100 A x 1.25.(In the NEC, "continuous" is defined as load lasting for three hours or more.)
So if you have to de-rate for number of conductors in a conduit, ambient temperature, etc, the final calculated conductor rating must still satisfy the 125% (of continuous load) requirement.
The breaker rating for a 30A load is 1.25 x 30A = 37.5A, then I will choose a 100AF/40AT, 3P, MCCB. Then the maximum continuous load for this breaker will be 32A which less than 32.5A derated conductor ampacity.
Obviously, the cable size, after applying 0.5 deration, does not comply or maintain the 125% rule. Is the reason why the 125% rule on the breaker adopted to be maintained on the conductor sizing so that the resultant conductor ampacity will always be higher than the breaker trip rating?
If the derated ampacity is 32.5A and for some reason, the load current went up to 34A, is the breaker with an ampere trip rating of 40A but can only carry continuous load of 32A going to trip through its O/L element? Will a 80% rated breaker of 40AT will not protect the 32.5A derated conductor with O/L from 32.5 up to 39A?
I apologize but I am still getting mixed up with the logic of maintaining 125% in addition to the derating factors in cable sizing directly related to the breaker capability.
The 125% requirement is basically to ensure that the circuit breaker is large enough to carry the load. The conductor has to be protected by the breaker,so they go hand in hand.
In theory, if you have 34 A load that lasts forever, a 40 A breaker could eventually trip.
Also, if you are derating the conductors for ambient temperature, give a thought to the circuit breaker - that equipment has temperature limits as well.
I just read from the NEC 2008 section 215.2.(A).(1) states that "....The minimum feeder circuit conductor size, before any application of any adjustment or correction factors, shall have an allowable ampacity not less than the non-continuous load plus 125% of the continuous load". This exactly what dpc states earlier.
Just an observation, I noticed as well that the CEC code, particularly section 8-104.(6) states otherwise. The section states to compare the one calculated with 125% and the one calculated based from de-ration and choose the one that yields the greater conductor size. Any comments?