hi everyone...

what will happen if i connect a current transformer of ratio 600/5 in a line that the full load current is 150 Amp?

and what will happen in case of full load current is 600 Amps and CT is 150/5?

Regars

xuxu

RE: curremt transformer

1) You will get 250mA of secondary current

2) In theory you would get 4A of secondary current. In practice and depending on what the specification of the CT is: possibly core saturation; possibly damage to the secondary winding; possibly both. With a low enough burden and a generously designed CT, possibly nothing untoward would happen.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: curremt transformer

Scotty--

He said 600/5.  150 amps in = 1.25 amps out.

For 600 amps in a 150/5, the secondary current is is 20 amps.  Okay for short time, but not continuous duty, assuming, as you said, you don't get into saturation problems.

old field guy

RE: curremt transformer

For 600A into a 150:5A CT, the impact depends on the rating factor of the unit. In the US, it's quite common to see RF 4.0 for metering CTs at this ratio.

If the RF is less than 4.0, then you run the risk of damaging the CT thermally if left continuously.

 

RE: curremt transformer

OFG,

Maths was never my strong point. Not at work anyway... blush
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: curremt transformer

Price2008

1. If you connect a current x'mer with 600/5 ctr in a
   150 amps load, then you will get two readings.
  a.1.25 amps when reading is taken in the secondary
   winding leads.And
  b.250ma when reading is taken from the 5amps relay.
2. And for 600amps in a 150/5 ctr, as OFG said, you will get
   20amps.of secondary current and 4amps when reading is taken from a 5amps relay.
    hope this helps.
                          

   










 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources