I did an infra red inspection on one 6,6 k V 3 cores XLPE Cable entering my 6,6 k V panel. There is nothing wrong on the terminal connections to the panel and nothing wrong either on the transformer terminals connection. The inspection is showing that part of the cable is heating as shown in the attached.
Grateful to have inputs from the forum.
Regards.
Grundig
I did an infra red inspection on one 6,6 k V 3 cores XLPE Cable entering my 6,6 k V panel. There is nothing wrong on the terminal connections to the panel and nothing wrong either on the transformer terminals connection. The inspection is showing that part of the cable is heating as shown in the attached.
Grateful to have inputs from the forum.
Regards.
Grundig






RE: IR Inspection
RE: IR Inspection
How did you conclude no problems at the connections near the top (cable to busbar and busbar to bushing)? Thermal survey with panel cover panel removed? If so, do you have that thermal image available ?
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: IR Inspection
Keith Cress
kcress - http://www.flaminsystems.com
RE: IR Inspection
I did infra red inspection on the transformer bushings and nothing abnormal were found. The connections to the panel were checked physically and found tight. We could not do infra red inspection on the terminal connections as the inspection guy was scarced to do the test with the panel opened.The infra red could not be done as the panel connections are isolated through a perspex sheet.
Regards.
Grundig
RE: IR Inspection
I couldn't see your picture clearly. Anyway, have you checked the current (Ampere) of each phase ? If all the measurement shows almost equivalent results, then I believe that won't be any big issue.
However, it's very hard for you to determine the temperature differences at the bushing's surface, coz' it's made from porcelain. Furthermore, the temperature may be affected by other factors. The best, you may measure the temperature at the connection of bushing, if it is exposed and not blocked by any object, e.g perspex.
Hope it's help. Please update us. Good Luck.
RE: IR Inspection
Steven C
Senior Member
ThirdPartyInspections.com
RE: IR Inspection
RE: IR Inspection
RE: IR Inspection
Keith Cress
kcress - http://www.flaminsystems.com