min embedment length for anchor rods?
Can anyone point me to a reference? Assuming strength works of course. I have heard 12*d as a rule, but haven't found any documentation...thanks
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
RE: min embedment length for anchor rods?
Tension splices/embedment lengths tend to be larger than a shear load.
RC
All that is necessary for the triumph of evil is that good men do nothing.
Edmund Burke
PIP standard
or Design of Anchor bolt design for petrochemical facilities..
Strength and embedded lengths are related because the strenth is the smaller of tensile strength of bolts or pull-out resistance.
However for shear there is recommended 10d or 12d spacing requirements either from concrete edge or between bolts because of the conical failure mode. If the bolt is too close to edge then it will spall off in shear or if the bolts are too close to each other then there is overlapping of critical regions.