Infra red flicker detector causing false flame failure
We recently installed a Weishaupt Natural Gas burner on a Petersen bread oven. The Weishaupt use an infra red flicker detector. If the load is between 90% to 100% load the flame signal is steady between 92% and 96%. Once the load modulates below the 90% range the flame signal bounces momentarily into the high 80% range and we occasionally get a flame failure. We have tried repositioning the scanner, adjusting combustion pressures, however it seems the detector a
Siemens Infrarot-Flammenfühler QRI 2 B2.B180B reacts too quickly to the modulating flame and is the cause of the flame failures.
Has anyone run into this problem before with an infra red flicker detector?
Cheers,
Bob Craig, Carmichael Engineering
Cheers,
RE: Infra red flicker detector causing false flame failure
Good luck
Jimmy