I have to detail an opening in an existing tiltup (two story building).
As yet, the locations are not known but i think they will be about 10 feet wide.
 
I have thought of two senarios,

1-the opening falls within the width of the panel,
2- the opening falls at the joint between two adjacent panels

I am a "non-building" structural person. So, I would really appreciate it if anyone wants to share an experience or suggest a reading source, codes..etc.

Many thanks.

FM


 

RE: Doorway Openings in Existing Tiltup Walls

Are the panels bearing or non load bearing panels and if loadbearing where in relation to the opening?

RE: Doorway Openings in Existing Tiltup Walls

I have inserted a plate as tension reinforcing previously, or a toes up channel... But 10 feet is a fairly significant opening! You might want to just frame it out with a welded steel frame, packed into the cavity with dry pack.

Also bear in mind the bearing during construction!  (Pun intended)

Cheers,

YS

B.Eng (Carleton)
Working in New Zealand, thinking of my snow covered home...

RE: Doorway Openings in Existing Tiltup Walls

On larger openings I have framed behind the panel using T.S.'s bolted into the panel.  The size and number of bolts for the columns based upon VQ/I (to account for wind or seismic) and the bolts for the cross beam based upon the gravity load involved.

For the opening at the joint between the panels, make sure that the panel is bearing on a continuous footing and not sitting on individual spot footings (or if it is, make sure there is enough of the panel left sitting on the spot footing to handle the vertical load.  

In either scenerio, the amount of panel remaining must be sufficient to handle the gravity load (unless you provide another arrangement to support the gravity loads) and the additional framing supplied would be designed to handle the lateral load.

Since , in tilt up, the walls generally provide the lateral stability for the structure, make sure there is enough panel left for your lateral loads.   

RE: Doorway Openings in Existing Tiltup Walls

I hope you are trying to do this on your own, without an engineer! Before you detail it, get a structural engineer involved. He can give you direction on what is required. The previous comments are things that your structural engineer need to consider.  

RE: Doorway Openings in Existing Tiltup Walls

(OP)
Thanks everyone.

JD2, you have suggested exactly what I was throwing around in my head. Thanks.





 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources