Reactor Sizing

Reactor Sizing

Reactor Sizing

(OP)
I came across late 50's low voltage MCCs and noticed all of the MCCs have reactors(current limiting) in series (between the incoming from the transformer to the line side of MCC) or MCC feeding another MCC. There are no nameplate or information available what so ever. Is there a way i can approximate the size of the reactor either by measuring voltage and current? if so what will be the better way to do it?
Regards.

RE: Reactor Sizing

In theory, you could measure the current flowing into the reactor and the voltage drop across it.

It might be safer to take one out of service and do this under  controlled conditions with appropriate test equipment.  
 

RE: Reactor Sizing

You should be able to derive the value of the inductance from the properties too (radius, # of turns, wire size).


ePOWEReng
www.ess-engineering.com

RE: Reactor Sizing

You are inserting a reactor so that you can reduce fault currents from a higher short-circuit rated bus ISChigh to a lower SC rate bus ISClow!
Having said that, all you need to do is find the difference in the short-circuit rating of the source bus and the supplied bus short circuit rating(in kA). With your bus voltage, you can calculate for the value of the reactance XL(assuming a pure inductive reactor) by dividing the rated bus voltage by the difference in short circuit amps. Be sure to use per phase values to arrive at the value of the reactance. Now you have the inductance L:
L =XL/(2 X Pi)X freq)

RE: Reactor Sizing

ee7860-

The only true way to find the inductance rating of the reactor is to measure the inductance, either by taking out of service and using an RLC meter or by taking inservice measurements of voltage and current. Note you'll need to get the phase angle as well.

You won't be able to tell the short-time current rating of the reactor from this measurement or the continuous current rating. If you're wanting to buy more reactors for a new install, then, as burnt2x said, you can figure ratings based on the formulas given. Note that when you size the reactor, use the short-time rating after the reactor is installed and not the rating prior to install...this could save some big $. I see people all the time over-rate current limiting reactors as they use the available fault current without the reactor for rating the reactor itself.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources