Periodic test of firefighting pump
Hello guys,
we have a centrifugal horizontal pump for firefighting service in our plant. As far as I know we should periodically carry out tests on our pump in order to guarantee that it is in good condition.
What I would like to know is : which is the parameter I should verify in terms of flow-head of the pump? I think that we should see that on 150% rated flow the pump gives us more than the 65% rated head, but which head? total head or differential head?
The fact is that we have in our system a little more suction pressure than the one which has been supposed in the design then it is possible to reach more pressure at the discharge even if the pump is not like if it were new.
Finally, the procedure of this test is available in NFPA 25?
Thank you so much for your help,
Marc
Marc
RE: Periodic test of firefighting pump
Section 8.3.3 Annual flow test.
Test the pump at or near the NET pressure and flow at Churn or shut off pressure, pump rating @ 100% psi @ 100% gpm , and 65% of the psi @ 150 % rated flow. The pump flows and pressures should be with in 95% of the rated flow and pressure rating of the pump.
See this web site on how to graph the test results
htt
h
http
Fire Sprinklers Save Firefighters' Lives Too!
htt
http
When you say NET pressure, you mean then the pressure at the discharge of the pump (suction pressure+differential pressure)?
I am from Spain and here maybe it's not as easy to find this kind of information, again thank you so much!
Marc
BUT you r complete system should be inspected by a company that does annual inspections of fire protections systems.
If you want to do periodic inspections that is fantastic.
Yes discharge pressure minus suction pressure = net pressure. The pump rating MAY be on the pump IF it is a UL or FM listed pump. These ratings are what you are comparing the pump performance to each year.
Marc