I have a Westlock Quantum 3600 Series position switch box with pneumatic solenoid fitted to it. It is mounted to a ball valve actuator. This assembly is certified to ATEX EEx"i", instrinsically safe. Problem is that the box has only one cable entry hub. We have two cables routed to this unit, one with 24 VDC solenoid control and the other for the status output from the switches, also 24 VDC. CablesCan I add a standard conduit fitting such as a Crouse Hinds GUAT, nipple mounted to the existing hub on the Westlock, fit both cable ends to the two other hubs on the fitting and pigtail the wires into the Westlock? I do not want to change out the Westlock and I cannot rewire the site to bring both control and status in one cable. I just need to physically be able to create two cable entries from one.

RE: Intrinsic Safe Wiring to Instrument

I gather that the switches and solenoid are all intrinsic safe, are the signals as well? You cannot mix IS and Non IS wiring (in NA anyway).
If it's not a hazardous location no problem, just use a tee or small box to combine 2 cables into 1
Roy

RE: Intrinsic Safe Wiring to Instrument

(OP)
Roy, Thanks for the prompt response. The area is hazardous, and the components, solenoid valve and limit switches, are all I.S. The GUAT would be a standard NEMA 7 box but I don't think that comes into play for I.S. construction; just mostly a robust electrical component.

RE: Intrinsic Safe Wiring to Instrument

Valvepuke
If all items (S.V and switches) are IS,  do not see any problem.  You have to add the IS berriers (as per approved valve manufacturer IS drawinds) somewhere outside the Hazardous area,  Run the cables from there with no Junction boxes or with J.B's with only IS equipment connected there, and enter into the valve with one multi-core cable or two cables entering a small box at the valve cable entry.
 

RE: Intrinsic Safe Wiring to Instrument

As iIan7 says, a small box or a conduit Tee since there are no terminations required (the wires go straight to the Westlock).
Another way would be to mount a small NEMA 4 box adjacent to the valve then run both cables through a length of 1/2" flexible conduit. That makes it easier to remove and makes for a neat installation. Coil up some spare wire in the box. Leave the inner jacket in place to prevent the shield touching ground.
If you need vapour seals to prevent gas migrating to the safe area they can be between the cables and box.
I don't believe you need NEMA 7 in this case (non sparking or intrinsic safe)
Roy

RE: Intrinsic Safe Wiring to Instrument

Don't forget the marking.  Few US projects are IS although some aspects such as the thermostat in an analyzer shelter may require barriers.  Assure that you include the required labels, special colors etc. to identify intrinsically safe circuits and segregate from all other conductors.

RE: Intrinsic Safe Wiring to Instrument

I too agree that if the 24V stuff has come thru a barrier you can punch more holes in you box with no issues.  You could use a non-sparking hatchet to do it even.  The safety is in the 'intrinsic' not the enclosures.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Intrinsic Safe Wiring to Instrument

IS by definition stated that the components within the enclosure do not store enough energy to cause ignition. Adding extra cable entries does not effect the IS rating.

I trust this helps,
Mlv
http://www.coulton.com

RE: Intrinsic Safe Wiring to Instrument

If Westlock put the I.S. label on it and shipped it with the solenoid attached, and particularly if the solenoid is called out in the model code, then the whole thing is I.S.
May need to be wired through approved barriers in a nonhazardous environment, but like Standingback says:no component stores energy.  

Consult your owner's manual, or download one from Westlock's website.    

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources