Utilizing Transformers at Other than Rated Voltages

Utilizing Transformers at Other than Rated Voltages

Utilizing Transformers at Other than Rated Voltages

(OP)
All,

I am looking for information on the affects of utilizing transformers at system voltage levels which differ from the rating of a transformer. For example: utilizing a 161kV/20.9kV transformer on a 161kV/22.8kV power system. What will be the consequences?

Any references, papers, etc. would be appreciated.

Thank a bunch for your help.

RE: Utilizing Transformers at Other than Rated Voltages

Well, if you use the nominal taps your voltage will be low.  How about a bunch more information about why you are asking the question and maybe you can get meaningful answers.

RE: Utilizing Transformers at Other than Rated Voltages

(OP)
I have heard that if you have a spare transformer but the voltage(s) does not quite match your system, sometimes it can still be used. I was curious if there were any "rule of thumbs" or calculations you could perform to determine if a transformer is acceptable to use in this way and how it would affect the performance of the transformer.  

RE: Utilizing Transformers at Other than Rated Voltages

Most transformwers have no-load taps that can be used to correct for off nominol applications.

RE: Utilizing Transformers at Other than Rated Voltages

So does your hypothetical 161kV/20.9kV transformer have a tap that would put it closer to being a 161kV/22.8kV transformer?  Better detail make for better answers.

RE: Utilizing Transformers at Other than Rated Voltages

If your 20.9 Kv system and 22.8 Kv system are not interconnected,nothing will happen and you can use as such.If you are connecting together ie parallely operating, a circulating current  among trfs will flow so as to reach a common voltage.Details of calculation-see IEC 60076-8 Application Guide for trfs.

RE: Utilizing Transformers at Other than Rated Voltages

You will get 20.9 volts instead of 22.8 volts.
The difference is about 8%. You may get close with adjustable taps.
In my little system the nominal voltage is 13,200 V. The most readily available distribution transformers are 13,800 V. (The closest large utility uses 13,800 V and that is what is usually in local stock.)
When a 13,800 V transformer ends up on our system, we get about 115V instead of 120 V. We sometimes leave it, and sometimes bump down the taps. It depends!
We avoid using different transformer voltages in three phase banks.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources