superconducting transmission line
3

superconducting transmission line

RE: superconducting transmission line

Very cool (literally), thanks for the post.  

RE: superconducting transmission line

Thanks for the link.

Great feat of engineering.

RE: superconducting transmission line

My firm performed the final acceptance test on that cable.
A very interesting project indeed.
Thanks for the link.  

RE: superconducting transmission line

dpmac

Any chance you can share what sort tests were conducted ?

RE: superconducting transmission line

Please do, i was wondering the same thing. What tests? Did they put continous PD monitors on this cable? What a shame if they didnt.  

RE: superconducting transmission line

Sorry I don't have more information, we only performed an after installation withstand test for the installer. Test voltage was 114kVAC for one hour. I am sure there were a number of other tests performed by others pertaining to both cooling equipment, cable and cable terminations.

There was a 34kV HTS installation in Albany NY a couple of years ago. We supplied an AC supply and HV Bridge so others could perform periodic PF tests as the cable was brought to final temp over a long period of time.  I believe a DC test was performed prior to installation on that project.

  

RE: superconducting transmission line

Thanks dpmac.

This is indeed an amazing development by US engineers. Kudos to them.

RE: superconducting transmission line

DC hipot?? Really??

RE: superconducting transmission line

Thanks for the link.
New generation!!!! Next step: transformer and generator?
 

RE: superconducting transmission line

ZogZog:

We did perform PD testing during the 60Hz AC acceptance test on the 138kV circuit.

Regarding the DC acceptance test on the 34kV circuit, they may have had other concerns besides PD on a cable of this type.  The insulation is not extruded and is operating at 65 Kelvin. I assume the possibility of space charges left over from DC testing was not a priority. I believe the mechanical stresses involved with the extreme low temperatures may be a bigger concern.

I will say the plumbing work involved with the cooling on both projects was very impressive!

RE: superconducting transmission line

I'm surprised at the "fault" aspect I'm reading here.

Used to be if a super superconducting cable got over amped -> the B-field got too large -> the cable went non-SC exploding at the first spot that went non-SC.

Now they're saying that it's a feature that limits damage and doesn't hurt the cable.

Keith Cress
kcress - http://www.flaminsystems.com

RE: superconducting transmission line

dpmac,

Sounds good, I missed the 34kV part.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources