Existing Wall Footing Modification
I am working on a job that has an existing 8" masonry wall sitting on a monolithic 16"x10" footing. The wall is about 25' tall braced at 24'. The wall is currently non-load bearing.
The owner wants to add 3 stories to the building and continue up from the existing masonry with new masonry. The wall will be load bearing in the new levels. I have checked the wall, and the existing masonry wall looks like it can take the additional load, but the footing does not have a chance of working.
the contractor wants to keep the wall, but remove the current slab-on-grade and replace with a mat foundation between the exisiting monolithic foundation for all the new columns we are adding for the new structure.
How can I modify the wall foundation to make it work?
The allowable bearing is 2500psf
The new wall load is about 6 k/ft
RE: Existing Wall Footing Modification
Never, but never question engineer's judgement
dgkhan I am not familar with underpinning, what is it?
Before I would explore these underpinning options, it might be beneficial to do some additional in-situ soil testing to see how conservative the 2500 psf is and see if can be increased.
The standard off the shelf helical pile is usually good up to 50kips (depending on soil).
Check out
http://w
I would consider underpinning with 4" diameter pipe pile, installing a lateral pilecap under the existing footing, with one pile inside the building and one pile outside, all spaced per the bearing capacity recommendations of a geotech.
Mike McCann
MMC Engineering