Fire alarm horn/strobes required in warehouse?

Fire alarm horn/strobes required in warehouse?

Fire alarm horn/strobes required in warehouse?

(OP)
I am looking at another engineer's design drawings for a warehouse facility and do not see any horn/strobes anywhere in the building.  Is fire alarm notification not required in warehouses?  From looking in the IBC I did not see any exceptions in section 907.9 for this type of building?

RE: Fire alarm horn/strobes required in warehouse?

I'm assuming:

- your warehouse is clssified as a Group S-1 occupancy
- the warehouse is used for high-piled combustible storage and has an area > 12K square feet
- the building is equipped with an automatic sprinkler system
- you are reviewing the 2006 IFC.

Based on these assumptions IFC Section 907.2 (same section in the IBC) does not require a manual fire alarm system nor does it require alarm signaling devices.

If your warehouse is a mixed use occupancy (e.g., B/F-1/S-1) or its a Group H, or its not sprinklered and being used for high piled combustible storage, advise me because the fire alarm and detection system requirements will be different.
 

RE: Fire alarm horn/strobes required in warehouse?

It is not unsual in many jurisdictions for the building drawings to not have a fire alarm system shown. These are typically designed by the installing contractor.  The cover sheet of the architectural drawings should have mentioned the need for a fire alalrm system.  I usually issue a phased approval until the fire alarm (and sprinklers also) working plans are submitted.  

Don Phillips
http://worthingtonengineering.com

RE: Fire alarm horn/strobes required in warehouse?

Depends on where you are. I've seen EEs doing FA layouts on TIs - some projects go that fast. And, he didn't tell us what he was looking at. I'm assuming he's doing a due diligence on some shop drawings.

And I question a lot of architects on a lot of things. His question is valid since the codes do a pretty poor job of saying "its not required." It would be nice if a design professional could open up the IFC, look up fire alarms in Group S occupancies and see the phrase "no requirement for a fire alarm."

I wonder how many consultants would be unemployed with such simple, concise language?  

RE: Fire alarm horn/strobes required in warehouse?

(OP)
It is a mixed use facility.  The storage is S-1, in addition there is a manufacturing area that is an F-1, plus there is a small portion of the warehosue that is an H classified area. The entire building will be sprinklered.

In light of those facts, section 907.10.2 Audible Alarms in the IFC, states that audible alarms are required.  I don't see anywhere in the IFC that gives an exception to this requirement (except that visuals may be used in lie of audible alarms).  

 

RE: Fire alarm horn/strobes required in warehouse?

Did you start at section 907 IFC

s-1: not required

f-1 Not required till over 500

H: required for H-5

So unless the building meets the above or system required for other reasons besides monitoring nor a/v inside is required.

Read the entire chapter do not skip

RE: Fire alarm horn/strobes required in warehouse?

Some conflicts that I can think (off the top of my head) of are with NFPA 101 and ADA rules that address areas that are "public areas" (as in 2 or more persons) should contain notification equipment


I am going to do some research (i have been working in the fire sprinkler field lately) so I will that this as a good opportunity to brush up on some of my fire alarm knowledge.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources