Is a failure of a 4-20mA transducer to the 20mA output a credible failure mode?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
4-20mA transducer failure to 20mA
|
RE: 4-20mA transducer failure to 20mA
It could do just that if there is an internal calibration mode that happens to get activated. But otherwise, I can imagine 0 mA 20+ mA or some intermediate value. But not exactly 20.00 mA.
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: 4-20mA transducer failure to 20mA
What is input and what %of input is applied?
RE: 4-20mA transducer failure to 20mA
RE: 4-20mA transducer failure to 20mA
2> Some transmitters (mostly temperature) will ramp upscale if a connection to a thermo couple or resistance temperature detector is broken. A 100% temperature indication will close the heat input and set the high limit alarms. This is a safe course of action when reliable instrumentation is lost.
This is not meant in any way to contradict Gunnar. His comments are accurate for an internal failure in an instrument.
3> Some controllers are programmable. You may select upscale or down scale in the event of a wire break.
eg: 0 ma in may = 4 ma out, OR 0 ma in may = 20 ma out.
Some controllers do not take special action on 0 ma in.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 4-20mA transducer failure to 20mA
The European user's group NAMUR actually has a standard for failure mode, typically configurable as 'high' or 'low', to something around 21mA or 21.5mA, I don't recall exactly, or about 3.5mA on the low side.
A number of other pressure transmitters use the same scheme but don't use NAMUR values/numbers. I seem to recall one brand that drove high to 22mA. I don't have access to those notes at the moment, but using 'outside' the normal range' fault modes might be worth considering if you're in the planning stage.
Dan