Lateral Pile Loads P-Y Curves LPile/Com 624
I'm in the the pile design phase for an integral abutment single span (130') bridge. LRFD per AASHTO. The subsurface exploration has been completed. We have slightly to moderately overconsolidated alluvial or lacustrine clays to 45 feet underlain by very dense sand and weathered shale. The clay appears to be reasonably uniform although there are sand "stringers" throughout-SPT results show some stiffer and softer intervals. Water table is about ten feet below abutment elevation.
Driven piles in a single row are the preferred choice of our structural engineer. Since I am confident of the end bearing stratum, my uncertainty lies with lateral load properties of the piles.
Laboratory testing on Shelby tube type samples has consisted of several consolidation tests (to confirm our choice of deep vice shallow spread footings and to evaluate embankment settlement magnitude and two unconfined compression tests. Results Su=1.2 KSF @22 feet and 1.8 KSF @ 32 feet.
Per FHWA NHI-05-042 and the COM624 manual we could use this data to assign K and e50 values for P-Y curve generation and proceed with the analysis. I understand LPILE offers the same approach albeit with an easier interface.
Does this approach provide sufficient accuracy and conservatism in our lateral loading analysis? Would we gain anything by performing three or four CU triaxes to obtain "better" data? My fear here is that non-uniform strength in subsurface will give us data scatter that will not provide p-y curves of any greater accuracy than those assigned based on C value in the literature.
If we proceed with program generated p-y curves based on C values, what type of parameteric exercise should be performed to assure conservatism at both ends of the spectrum?
Thanks in advance.
Thanks in advance.
RE: Lateral Pile Loads P-Y Curves LPile/Com 624
Even if the stratified soil results in non-uniform p-y curves, the resulting shear, moment, and deflection of the pile will be "averaged" over the length of the pile, so the results won't be that much different from using the "average" p-y curves.
Good luck