Question on moment arm for analysis/design
I hope I don't come across foolish here, but I'm having a hard time understanding something. Let me explain the sketch I've posted before people start tearing it apart. This is not an actual detail, it is merely to help get across the point of my question.
The question is if you have a detail similar to this (whether it is a beam to column, or a column to ftg), would you use d for the moment arm to design the tension in the top anchor or (approximately) d+2g ( I know it would be from the top anchor to the centroid of bearing at the bottom angle, but just for argument's sake say d+2g)?
Does your answer change if you provide stiffeners such that the angles can be considered very stiff?
I'll give my opinion and explanation, then you can tear that apart.
I think you should use d as the moment arm in either case. I am differentiating this from a baseplate because a baseplate is a single (considered rigid) element that has a moment applied to it. This detail (whether stiffeners are present or not) has two individual angles with a tension and compression force applied seperately at a given location. While the baseplate is seeing 0 net force, moment only (assuming moment only and no axial load), these angles are each seeing a tension (or compression) force via the weld (not a moment only with 0 net force like a baseplate). I believe this applied whether the angles can be considered infinitely stiff or not because of the above reasons and the fact that they are so close to the end. If the angles were WT's and extended for some distance into the span of the beam such that the WT's had the opportunity to become fully engaged in helping to resist the moment, I would feel differently, but the angles (as they are currently shown) do not have that ability.
Any opinions?
Any opinions?
RE: Question on moment arm for analysis/design
Technically one of the lines of anchors will not be taking load and it will be a compressive force on the brick/concrete but I have found it is usually conservative to take loads at the anchors.
The real answer is somewhere in between. Free body diagram is a vertical beam with a plastic pin at the bottom compression flange and a plastic pin at the tension anchorage with a tension load at the top of the beam.
I agree for a flexible angle, but you can make the angle stiff enough to neglect prying by following the procedures outlined in the steel manual of providing the stiffener. I am more concerned with which moment arm to use.
Free body = pin support at the bottom of the compression flange; Tension force at the top of the tension flange; reaction at the wall anchorage
As shown, I would base the tension on d+g. The flange with the compressive force will transfer that force to the wall in compression through the angle leg parallel to the flange. I suppose one could adjust for half the thickness of the flange.
I think you wanted to eliminate that bearing action by adding nuts between the angles and the wall. Sort of, like leveling nuts under column base plates without grout. In that case, I would agree with you that the tension/compression forces in the bolts would be based on T/d. The apparent difference in couples is taken by the moments in the welds connecting the angles to the beam. If you draw a free body of each angle, you see that you need a moment in that weld equal to T*Δy.
Mike McCann
MMC Engineering
If you believe that the tension in the bolt is less than the shear in the weld where does that force go?
I guess I am picturing a FBD of this angle with a Tension force in the horizontal leg of T1=M/d (pointing to the left), and a horizontal force from the anchor of T2=M/(d+g) (pointing to the right). T1 > T2 and the only other force that can be present is the top of the angle bearing on the wall as it tries to rotate, but this will only add to the forces pointing to the left.
I am failing to see, just by statics, how the force in the anchor can be less than that in the weld (i.e. how T2 applies).
The difference lies in the difference of the moment arms...
It is true that the moment arm for the welds is "D", the distance between the welds and the depth of the beam.
However, assuming that the thickness of the angle is enough to transfer the weld force to the anchor bolt without bending, then the effective moment arm of the connection to the bolts is increased by a distance "g", the gage dimension. If the angle fails, then you have a connection failure. As this is not what we want design for, the angle must be designed to transfer the force without failure.
Mike McCann
MMC Engineering
The attached sketch below is for a stiffened condition. To achieve the "rigid" condition, the welds now must take not only shear but moment along the horizontal leg length. This creates a force at the bolts = M/(d+2g) which is also the shear at the welds. The shear at the welds is no longer M/d since there are new moments at the end of the beam that change the total moment to something less.
That's because it isn't, shear remains constant, based on the (d+g) moment arm.
(Assuming there is no prying.)
I understand the concept of prying and the additional force it exerts on the bolts. I made a pretty slick spreadsheet using the prying equations for wind moment connections.
The shear will only be M/(d+2g) if the bottom angle is very stiff, eg. by using stiffeners or the like. I would use (d+g) in my design unless there is a very good reason not to.
csd, miecz, msquared, and JAE have all stated that the welds should be based on the "d" dimension. JAE has added the qualification that this would only apply if the angle is not rigid.
I believe the force in the tension in the bolt is equal to the shear in the weld but the shear in the weld is less than the force in the flange beyond the weld. Where does that extra force in the flange go? It goes into the web of the beam. It gets there as a couple thru the weld. Looking at JAE's second sketch, you see that moment shown as T'a, where T' is represented as perpendicular to the flanges. Once in the web of the beam, picture the 2 couples in the web with forces parallel to the flanges. Those forces are the difference between the force in the flange and the shear in the weld.
Referring to JAE's first sketch; obviously one of us is wrong, at this stage I don't believe that it is me.
I'll try to explain. The lever arm is the distance between the points of compression (C) and tension (T) reactions on the connection.
The location of C depends on the stiffness of the bottom angle; it's either at the bottom flange or near the bottom bolt.
The location of T is always at the top bolt, it makes no difference if the top angle is flexing or not.
The the reactions will then be M/(d + ~2g) -- I use approximately because of the compression reaction need not be located at the bolt centroid, but it is easiest to talk about it as if it does.
The shear at the welds will be equal to the reactions. Try drawing a V-diagram as though the angle-beam-angle were a single member loaded with two point loads at the beam flanges. These loads would be equal to M/d - with opposite signs. (Alternatively, you could load it with a single moment at the center, but I don't think it illustrates what is going on as well as the force couple)
I don't agree that the force in the weld is based on M/d. I merely referred to JAE's excellent sketch. It's true those forces are are represented as a vertical couple, but once in the web, that couple becomes a moment, and that moment adds force to the flange, so the flange force beyond the weld is greater than the weld shear, which is equal to the bolt force. This model, of course, ignores some secondary effects, such as the bending stresses in the web beyond the weld.
isn't d+g (or d+2g) only the lever arm at the section where the angles connect to the wall? It is not the moment arm 2" away from the wall where the angle leg is welded to the beam flange.
I guess I am having trouble visualizing the flow of force. I am picturing a short cant with a moment only applied (either a moment or a force couple at the flanges). Either way, the moment is flowing out of the beam, into the welds, through the angles and ultimately to the wall. It is not starting with the wall and working its way backwards. When the forces are transitioning from the beam to the angle (via the weld), it doesn't know whether the anchor to the wall is 1" up or 100' up. In the attached sketch, would you say that the weld is taking moment only (per JAE's second sketch) and virtually 0 tension/compression into those angles? I wouldn't.
True, but just like any other structure, you solve for external reactions based upon the stiffness of the structure, then cut free body diagrams to get internal forces. Another example, in a continuous beam a load on one bay doesn't "know" if the beam is simple supported or if there are several supports. The load "goes" where the global stiffness of the structure dictates.
BTW, how do you quote in a response?
Thank you all for the discussion and bearing with me with stuff like this. I really can't ever take anything for granted and I really NEED to understand the why and how.
Thanks a bunch!!!
Also, if anyone has time to comment on the sketch I recently posted with the weld of the tip of angle to tip of flange, I would appreciate it. I don't believe there is an opportunity in that case for the weld to develop moment.
1. The angles, by design, will most likely be the same size for ease of construction. That being said, and also assuming that the angles will not be allowed to go into the plastic range, then the legs will not yield. Hence the design moment arm will be closer to the d + 2g, not the d +g that I previously mentioned.
2. The use of d + 2g is less conservative than the use of d + g for the tension in the bolts, and even less conservative than d.
3. The tension is seen in the bolts, and the compression in a compression block of varying stress on the flange of the opposing angle bracket. Tis is true if there is no back plate at the end of the beam. If there is a back plate, then there is a larger area triangular stress block that starts below the bolt in tensoion and proceeds to the limit of the lower angle flange.
4. Considering comment 3, the moment arm value of d +2g is only an approximation of the true moment arm.
Mike McCann
MMC Engineering
Agree with your analysis except for one major point: The "V" that you calculate is the force in the flange to the left of the weld. The force in the weld is M/(d+2g). It has to be, since, if you take a free body of the angle and sum forces in the x direction, the shear in the weld has to equal the force in the bolt.
I agree. I mis-spoke when I said the total shear in the weld. What I really meant to say was the total load in the flange (some from the direct shear in the weld and some from the moment in the weld).
The horizontal shear in the weld will be m/(d+2g), but there will be a vertical component required to add to it vectorially. So that being said, I would still probably just size the weld for M/d (to keep from having to calc the moment in the weld and add the shears vectorially), and size the anchors for M/(d+2g)
Note that I'm showing it to be M/(d+g) only because I assumed the lower angle to be flush against the concrete.
If you "heard" it on the internet, it's guilty until proven innocent. - DCS
The beam has a flange force equal to M/d (or more precisely M/(d-tf)). This will be the shear force resisted by the weld, and this is the tension I would use for the anchor. I see the flange force going through the weld into the angle, then through the angle (bending), to the anchor.
This beam has a moment, but let's say it had no moment, only tension on it. Let's make this total tension equal to 2*M/d. Assuming the flanges take all the tension, this gives a flange force of M/d, the same as my suggestion above for the moment.
So far, the top flange has virtually the same stress in each scenario. If the top flange is loaded to full stress, it doesn't really know if the bottom flange is at the same stress, or if it is at the reversal of that (T/C).
For the axial case, beam loaded in tension only, nobody would question that the anchor sees half of that tension force, or M/d.
I contend that these situations are the same, and the anchor tension would be M/d for the moment case.
The two cases are not the same. The moments due to T'd and C'd (see above) are additive in the case of an applied moment. These moments cancel each other in the case of a tensile force.
1) the moment due to P can be reacted due pin loads on the two angles ... moment arm = d+2g. this imples that there is a moment on the welds between the angles and the beam (consider a FBD of the angles, the offset in the forces ("g" apart) has to be reacted somehow).
or 2) the moment due to P is reacted by a couple at the welds to the angles ... moment arm = d. this implies that the angles have a small moment reaction to the rest-of-the-world, again due to the offset in the forces on the angle (offset = g).
or 3) some combination of the above and/or some fussing with the reactions (is the compression reaction at the fastener, at the tip of the angle, at the base of the angle, ...)
Cut a section just left of the angles. The flange force in each flange will be M/d. This assumes all the stress is in the flanges, with none in the web.
Now go right a little, at the angles. At the interface of the flange and angle, the horizontal force, called T1 in JAE's sketch, has to be equal to M/d for the horizontal forces to be in equilibrium. This is independent of the T' and C' moment, which I haven't fully reconciled in my mind yet. Regardless, for the summation of forces in the x direction to equal zero, T1 must equal M/d.
Now go to the angle. The bottom force, T1, will have to equal the anchor force, T2, for the summation of forces in the x direction to be zero.
Finally, I'm picturing another free body diagram with only the top angle removed (we have beam and bottom angle, no top angle), with the total compressive force in the bottom angle resolved as a point load at the anchor. The only external force is the moment. There will be an internal horizontal force at the top flange to angle interface, T1, which I propose above is M/d. The only other horizontal force is the anchor force C2, which has to equal T1.
T1=T2=C1=C2=M/d.
"Now go to the angle. The bottom force, T1, will have to equal the anchor force, T2, for the summation of forces in the x direction to be zero."
sure the force into (and out of) the angle can be M/d, but the angle isn't balanced for moments as the forces are offset (by "g"). to satisfy the FBD, there would need to be a moment on the vertical leg of the angle (as originally drawn) to react this moment. also, these moments restore the overall FB balance; consider the FB of the beam and angles.
One thing that I sensed in drawing out the second free-body diagram was that the moment in the beam isn't constant.
My first thoughts on this were that there is an "M" in the beam that must be simply resolved through to the end bolts.
However, with the rigid angles welded to the end of the beam, I believe that the "M" that sort of comes in from the left, actually changes across the angle leg widths.
So you can't just say that M/d is the force in the flange because the M varies as you move from the left of the beam towards the end of the beam.
This is tough to visualize because we usually look at beams as single line sticks. This problem, to be correctly analyzed, would need an FEM analysis to really see what is going on since there are moments applied to the end of the beam at the left and at the top and bottom flange ends.
It's not instantaneously all taken out of the flanges. It is taken out along the length of the angle's horizontal leg. The average shear force in the weld is as shown in JAE's angle FBD.
I would design the anchor for that much smaller force. The weld would have a small shear, but a large moment. The weld would be designed per table 8-4, page 8-66 of the AISC Code, the lower sketch, with a large "a".
The the shear and moment diagrams explain what forces the parts are designed for. The extra force not accounted for in a free body of just the angle is the constant shear thru the beam web.
Is this model valid?
I suppose so, it's just not so intuitive.
Mike McCann
MMC Engineering
As for design, I'm with Mike, I would have used M/d and not thought twice about it.
I tried to make what you are suggesting theoretically happen and I can't. If the angles were only attached at the very toe to the beam with welds, and likewise at the very toe with a weld at the wall, then the shear at the angle's toe would be as you say (M/d). But the assumptions don't work with statics. There has to be a different force transfer between the angle and the beam when using the rigid angle assumption or the angle would be unstable.
I'm also impressed by how interested so many of us are in a topic as basic (or essential) as this.
I still believe that M/(d+2g) is potentially unconservative and therefore wouldn't use it.
A star to the originator.
Mike McCann
MMC Engineering
I would have designed the weld for a shear of M/(d+g), plus a moment of (M*g)/(d+g).