(OP)
I have a two story school I am designing that is apperoximately 320'x100'.  The structure is masonry loadbearing walls at the perimeter and along the interior corridor which runs down the middle of the building parallel with the 320' exterior walls.  The second floor is metal joists with non-composite metal deck + concrete, and the roof structure consists of steel joists and metal deck.  My question is if I need a building joint to break up the 320' length.  The loadbearing masonry walls have control joints about 24' on centers and the CMU bond beams are continuous through the control joints at the roof and the 2nd floor.

RE: Building joint spacing

Others will have different opinions, but I would place an expansion joint at mid-length.  And I would use control joints at 20' centres, with the bond beams discontinuous at the joints.

RE: Building joint spacing

You are going to need a shear wall in the 100' direction. You're not going to get the deck to work at a 3:1 aspect ratio. That's a good place to locate your expansion joint.

RE: Building joint spacing

(OP)
frv,

I do have a few shear walls in the 100' direction.

I was thinking I would not need an expansion joint because I have CJ's in the CMU.  I know the CMU walls will still have alot of stiffness at approximetly 24' in length, but I was assuming this would still allow for some expansion and contraction of the 2nd floor and roof diaphrams.  It can't be any more stiff than having a steel framed building 300' long with braced frames located at each end of the building.

RE: Building joint spacing

How much trouble would it be to put a building joint near the middle of the 320' direction?

IMHO, at 320' you are right at the 'do it/don't do it' line. If it was reasonably easy to put the joint in, I would do it and sleep well at night.

If it will be difficult to get the joint in, with some proper detailing, you can make the 320' work.

Without a joint,  I would tend to break my bond beams every 2 or 3 joints to allow some shrinkage movement by the CMU walls at the bond beam elevations.

JMHO.

  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources