Gantry truss - Column Base plate connection - Pin or Fix ??

Gantry truss - Column Base plate connection - Pin or Fix ??

Gantry truss - Column Base plate connection - Pin or Fix ??

(OP)
Normally , I have pin connection for portal frame or similar structure. However, I check the gantry truss say 16-30m span with the column pinned base connection, a large deflection occur compared to fixed based.

It seem to me that I have to use column base fixed connection.

 

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

You will always get larger frame drifts with pinned bases compared to fixe bases.

What is your question?

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

It may help if you explain what you mean by "gantry truss" and better define your structural system.  The word gantry is used in several different ways in structures.

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

As StrEIT wrote, what is your question?

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

(OP)
I model a 16m long truss supported by columns of 6m high. Pinned base columns give very high lateral deflection. I have to go for fixed based column to reduce to member size.
Then go ahead for rigid fixed base connection design.
Is it ok ?  

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

Sure, it's ok.  Why wouldn't it be?  Just be sure to design the baseplates, anchor bolts, pedestal/pier (if applicable), and footing for the required moment.

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

tngv752
It's not a particularly high building, do you know why the lateral deflection is high?
Maybe the columns are just too small?
There is nothing inherent in trussed rafters which would cause excessive deflection.

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

(OP)
It's not economic to increase the member size. Another solution is to put bracings but the client doesn't want it.

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

Where a column is nominally pinned to a foundation that is designed assuming that the base moment is zero, the stiffness of the base may be assumed to be equal to 20% of the column stiffness when calculating deflections under serviceablity loads. This may be done by introducing dummy members or spring stiffness at the column base. In the experience of the author, this will significantly reduce eaves deflections

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

parrot-

Can you post a copy of that paper or give the author and a ballpark date?

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

S..EIT,
The above post is based on guidence offered in The Steel Construction Institute (Berkshire U.K.)publication SCI P252 titled 'Design of Single-Span Steel Portal Frames to BS 5950-1:2000'

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

Other option to design a partially fixed base portal frame.

Analyse whole structure as pinned based for strength.

Provide a separate load case with a 10k.ft moment applied at each column base. This will give you the amount that the deflection is reduced for each 10k.ft of base fixity.

Use superposition to calculate what the required base fixity moment is to keep deflections at an acceptable level.

Design base to act as fixed at the serviceability level.

RE: Gantry truss - Column Base plate connection - Pin or Fix ??

StructuralEIT
Reference to the 20% base stiffness for defections can be found in Advisory Desk notes AD90, AD97 & AD194.
These can be accessed by doing a search on;
http://www.steelbiz.org

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources