Fire rated floor deck

Fire rated floor deck

Fire rated floor deck

(OP)
Does anyone have a detail for a load bearing metal floor deck fire rated 2hr from both sides.
 

RE: Fire rated floor deck

Any steel beams or just concrete over metal deck?

RE: Fire rated floor deck

(OP)
Steel beams fire sprayed, no concrete just metal deck///

RE: Fire rated floor deck

Bare metal deck without concrete fill has no fire rating. There is no tested UL assembly for bare metal floor deck with spray-on fireproofing.

The closest thing might be metal roof deck w/ spray-on plus roofing but you cannot use this assembly if you have no roofing.

I see no way that you can achieve the 2 hour rating as you are asking. I think that you might be stuck adding concrete plus spray-on.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources