LV MCCB/Contactor Insulation Resistance Testing
2

LV MCCB/Contactor Insulation Resistance Testing

LV MCCB/Contactor Insulation Resistance Testing

(OP)
Hello all. I would like to request in this forumn typical connection diagram for megger testing 600V MCCBs or contactors using 500Vdc megger.I do not have any connection diagram for this and any reference and links is appreciated from concerned tes professionals here.

Thank you.

RE: LV MCCB/Contactor Insulation Resistance Testing

(OP)
I have gone further and read some articles on this. The insulation resistance for a breaker are being done as follows:

1. Phase-to-Phase (each phase pair combination at line
   side and load side separately, CB is open)

2. Phase-to-Ground (each phase and ground at line side
   and load side separately, CB is open).

3. Across Each Phase With CB Open (IR measured across the
   open contact of each phase separately).

However, I came across another test procedure that states that the test done with one phase and the other phases shorted to ground and interconnected to the megger "earth" terminal.

Which IR test connection is correct, this one or the above (1,2 & 3) connection?  

RE: LV MCCB/Contactor Insulation Resistance Testing

Nightfox,

for low voltage power circuit breaker 3 tests should be done:

Phase to phase (A-B, B-C and C-A), breaker closed.
Phase to ground (A-G, B-G and C-G), breaker closed.
Across each phase (A-A', B-B' and C-C'), breaker open (of course smile )





 

RE: LV MCCB/Contactor Insulation Resistance Testing

Yep, and should be done at 1000VDC for 60 seconds and should be >100M

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources