Gents,

are you aware of any technical code that mandates Power Stations' Generator maintenance and electrical testing?

Thanks,

NC

RE: Generator Maintenance code

Do you mean the codes related to generator protection?
These can help you:

25 : synchronism check
40 : under excitation
55 : power factor correction
66 : motor start
87 : differential

-Said-

RE: Generator Maintenance code

Is the question stemming from the desire to differ the maintenance, if not required by Code? or are you looking for guidlines as to how to maintain power plant?

 

RE: Generator Maintenance code

(OP)
Seymainsaid,

The numbers you have mentioned are ANSI devices numbers. No I am not looking for that.  The question was pertaining to standards and technical codes with reference to Gen maintenance.  Regret that I was not clear enough.

Rbulsara,

I am trying to make / change schedule for maintenance  - specifically electrical tests for condition monitoring purpose and looking for document that provides guidelines for the purpose - other thatn OEM manuals.  Have consulted OEM manuals but they are not clear enough on the front.

Looking for best practices, Standards, Codes, regulations and any other material that is available.

NC

RE: Generator Maintenance code

I would recommend the following for generator maintenance:

daily:
check temps, pressure, purity of H2 or anything, bearing vibrations, look at collector for any arcing, seal oil system.

monthly:
perform shaft voltage testing, replace brushes as needed.

annually:
inspect general terminals for any leakage and clean bushings disconnect switches and any PT/CT if its mounted on top of the generator (GTE),

every 2 years:
minor inspection, high pot, elcid, insulation testing.

Regards,
Steve

check out
www.powerplantforum.com
lean. educate. network

 

RE: Generator Maintenance code

You can download the NETA reccommended frequency of maintenence tests for free at www.netaworld.org

RE: Generator Maintenance code

I am no large power plant expert, but generator is a generator.

What size generator? What is the type of prime mover? A lot dependeds on the fucntion/purpose and configuration of your plant as to what you can shutdown for maintenace and how often.

For any sizable power plant you will need to consult your counterparts or a forum consisting of power plant operators. If you are part of an established firm, there must be existing guidelines. If so, you should have very good reason to "change" them besides money and inconvenicece.  OEM recommendations are a good beginning. As Zogzog said NETA-MTS is also a good place to start.

You also need to coincide the electrical maintenance with mechanical (prime mover).


 

RE: Generator Maintenance code

For Hydro Generators - IEEE 492

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources