Transformers - Fire separation - Blast walls
2

Transformers - Fire separation - Blast walls

Transformers - Fire separation - Blast walls

(OP)
Where can I find guidelines as to what rating transformers require how much spatial separation to avoid blast walls.

Thanks.

RE: Transformers - Fire separation - Blast walls

Refer NFPA-70 Articles, 450.21,25,27

RE: Transformers - Fire separation - Blast walls

(OP)
Thanks ELEP. The Article 450.27 / NFPA70 does mention that the fire safety measures are required (my concern is with regard to outdoor, mineral oil insulated transformers of all sizes).
I am looking for some guidelines like transformer rating vs separation required between the transformers. In addition similar guidelines for fire-resistant barriers (blast walls) and fire suppression systems.

I have referred IEEE Std 979 Guide for Substation Fire Protection, IEEE 850 and NESC. But the guidelines are a bit general.

In India, there are guidelines issued by TAC (Tariff Advisory Committee of Insuarance compenies). But, the place I work now there is no such institution. Hence, I am looking for any such European or American guidelines.

Thanks.

 

RE: Transformers - Fire separation - Blast walls

If you have access to IEC standards then IEC 61936 contains some information which might be useful. Local codes may over-rule the IEC document recommendations.
 
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Transformers - Fire separation - Blast walls

(OP)
Thanks ScottyUK for reference to IEC 61936.
The code has a table, Transformer oil volume vs required separation distance and is exactly the info I was looking for.
Surprise that the same is not available in IEEE codes!

RE: Transformers - Fire separation - Blast walls

NFPA 850 - the fire protection standard for power plants has recommnedations for separation of transformers based on amount of oil.  Example: 500-5,000 gallons of oil, separate adjacent transformers by 25 feet or a blast/fire wall.  Over 5,000 gallons- separation is 50 feet.

The separation prevents spread of transformer fires to adjacent units or critical buildings.

Same information is found in some Factory Mutual Engineering guidleines.  Both of these organizations are insurance companies.

RE: Transformers - Fire separation - Blast walls

I work for a rural electric cooperative and our bylaws state that a transformer must be a minimum of 10 feet from the wall except if the wall has a minimum 1 hour fire rating.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources