Shell Test Pressure
Shell Test Pressure
Shell Test Pressure
This is what ASME B16.34 says:
7: Pressure Testing
  7.1: Shell Test
    7.1.1: Shell Test Pressure - Each valve shall be given a shell test at a gage pressure no less than 1.5 times the 38C(100F) pressure rating, rounded off to the next higher 25 psi(1 bar) increment.
I have a ANSI CL300 Check Valve Wafer Style NPS12". Operating Temperature - 288C
Operating Pressure - 336 psig
According to ASME B16.5 Table F2-2.2 for A351 Gr. CG8M, working pressure for CL300 at 38C is 720 psig.
Is it acceptable to use 450 psig as the shell test pressure in this case? If not, what should be the test pressure?
I will appreciate your insight in this. Thanks in advance.
Jaideep
RE: Shell Test Pressure
Are you the end user or the manufacturer of said valve?
I am the end user. The valve will be used in extreme conditions and the life expectance expected out of it is atleast 25 years.
Jaideepk;
Why are you even testing this valve, is this part of new pipe construction or repair, or are you looking to prove test an existing valve?
This is a newly manufactured valve that has to be hydrotested by the manufacturer as a requirement prior to acceptance.
The manufacturer is responsible and would follow their procedure for hydrotesting in accordance with ASME B16.5.
correction ASME B16.34, not 16.5 (flanges and flanged fittings).
Jaideepk;
By the way, if you are going to quote or paraphrase applicable paragraphs from Codes and Standards please make sure that you read and copy the necessary paragraph.
Regarding test pressure in this section (a)7.1, it is 1.5X the working pressure at 100 deg F using water. So go to the Pressure-Temperature rating table applicable for the material group and class valve. All of the information is there and as I mentioned above the manufacturer would perform this activity and know this as well.
