ANSI Current transformer ratings

ANSI Current transformer ratings

ANSI Current transformer ratings

(OP)
SR, DR and MR ratings of current transformers. How do they compare with IEC spec'd CTs?

Thanks

RE: ANSI Current transformer ratings

I believe that SR, DR, and MR refer to single ratio, dual ratio, and multi-ratio, not to ratings.

RE: ANSI Current transformer ratings

Hi Powercrazy:
jghrist is absolutely correct.  The abbreviations you listed are standard abbreviations for single ratio, dual ratio and multiratio C.T's.

Good Luck.
ANG

RE: ANSI Current transformer ratings

In IEEEC57.13, multi-ratio (MR) secondary windings are specifically defined (for 600:5A MR to 4000:5A MR).

In the IEC world, there is no specific definition of multi-ratio. Therefore, it must be specifically spelled out, i.e. 500/1000/2000:1A.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources