standpipe system
standpipe system
(OP)
Hello
I've come to wonder for my proposal to design highrise sprinkler system what is two-zone standpipe system? Why would it necessary to zone stanpipes in highrise buildings? Would a
20 story office building need the zoned standpipe system? Any experienced answers would be appreciated.
I've come to wonder for my proposal to design highrise sprinkler system what is two-zone standpipe system? Why would it necessary to zone stanpipes in highrise buildings? Would a
20 story office building need the zoned standpipe system? Any experienced answers would be appreciated.





RE: standpipe system
So you could have separate systems.
The lower floors could be off of city pressure and the upper floors off a fire pump.
Or you could have a fire pump on more than one floor - one to pump to the first 10 storeys and the second to pump to the upper 10 storeys.
RE: standpipe system