UL508 panel branch protection for multiple motors
I am designing a UL508 panel for industrial machinery. I'm starting two 50HP 230/3/60 motors with FLA of 116A each. I typically use Siemens Type E self protected starters, but due to the larger current rating I'm exceeding the highest amp rating of the series. I'd like to use a solid state Overload relay (Siemens 3RB10).
The specs in the catalog say that I will need to add extra short circuit protection for these overloads. Of course, I could add two fuse blocks with dual element J-fuses sized at 175%. I was wondering if it was OK to use one set of fuses to protect the two motor branches as per group installation rules. The UL508 code has section 66.7.5 that covers industrial machinery, but I found it a bit confusing. I'm thinking of 300A J fuses protecting the two motor branches. Other suggestions would be welcome.
RE: UL508 panel branch protection for multiple motors
I may have left something out, it's been a while now since I've done it and it seems to me that there were a total of 6 criteria that needed to be met, but I can't think of any more off the top of my head.
I'm embarrassed to admit it, but we have some 300A fuses and a fuse block from a canceled order that I am trying to use up somewhere. I thought, "Just maybe..."