hanging to trapeze ceiling
I have a question about hanging to trapezoid sheet. We will do a sprinkler installation in Poland according NFPA. Can we hang sprinkler pipe DN65 to trapeze sheet? I will use trapeze ceiling fixing. Could you show me any record in NFPA13 which say about hanging to trapeze sheet/ceiling?
Thanks a lot
RE: hanging to trapeze ceiling
Are you talking about a suspended ceiling supported by lightweight metal with dimensional lay-in panels?
1. substantially supported from the building structre
2. must support water filled pipe plus minimum 250 pounds
3. metal deck can support 1 inch or less
see reply above if you can meet some of those go for it
there are more specifics in nfpa 13
Check out the Sammy Xpress hanger.  It is listed for up to 4" pipe.  You need to make sure that the trapezoid sheet is of the proper gauge.
http://www.sammysuperscrew.com/sammyxpress.htm
Travis Mack
MFP Design, LLC