I have a fully sprinkled theatre.
One either side of the stage I am dropping down to a hose valve cabinet with 2 1/2" hose.
The overhead pipe is 4" and I do have to calculate the standpipe 500 gpm @ 100 psi but what is the minimum size for the drop?
I would like to drop 3" but it appears my minimum size is 4".
Block is going up and I need to do something out there this afternoon. Hate jobs I am behind on before I start.
One either side of the stage I am dropping down to a hose valve cabinet with 2 1/2" hose.
The overhead pipe is 4" and I do have to calculate the standpipe 500 gpm @ 100 psi but what is the minimum size for the drop?
I would like to drop 3" but it appears my minimum size is 4".
Block is going up and I need to do something out there this afternoon. Hate jobs I am behind on before I start.





RE: Theatre, 2 1/2" hose valves either side of stage minimum pipe size
I know you are in Georgia and they have their own amendments but the 2006 IFC, Section 905.3.4, exception 1, allows the use of a Class II standpipe when the building or area is fully sprinklered.
RE: Theatre, 2 1/2" hose valves either side of stage minimum pipe size
Yes, you are right but this isn't my design and the project engineer insists insists we have a 2 1/2" hose valve.