Hi
I am a junior engineer and need some urgent assistance.
I oredered some indoor switchgear from a switchgear manufacturer.INC FDR B/S.(NOT OIL)
I need to give indication witch test I need to see at the FAT and at the SAT.
I am aware of the following test that need to be happening,but is there anu additional test that I must request routine tests?
Insulation resistance
High voltage testing
Manual operation
low resistanceductor measurement of all busbar joints
primary injection of each panel
closing, tripping and sequence testing of control circuits
I am a junior engineer and need some urgent assistance.
I oredered some indoor switchgear from a switchgear manufacturer.INC FDR B/S.(NOT OIL)
I need to give indication witch test I need to see at the FAT and at the SAT.
I am aware of the following test that need to be happening,but is there anu additional test that I must request routine tests?
Insulation resistance
High voltage testing
Manual operation
low resistanceductor measurement of all busbar joints
primary injection of each panel
closing, tripping and sequence testing of control circuits






RE: 11kV switchgear commissioning
Have them test any protection relays that may be associated with this gear. This usually involves a doble test set which mimics current and voltage into the relay to ensure that it operates at its propper settings.
RE: 11kV switchgear commissioning
Having been in the business of commissioning switchgear myself for a bunch of years, please let me talk you into engaging a third party who does that sort of work, and have them work with you to develop a scope of work for your installation and then perform the work for you.
Over the years I have made a lot of money and consoled a lot of clients who trusted the manufacturer to test and install their equipment, only to find out years later that the manufacturer overlooked some critical test.
We had one client who chose the "these people built it so they know best how to install it" route. The manufacturer's field team neglected to connect a critical DC power wire, a fault did not clear, switchgear failed and the resulting fireball melted the concrete foundation of the equipment room. It's horror story, but it does happen.
old field guy
RE: 11kV switchgear commissioning
Look for a CERTIFIED 3rd party testing agency that follows NETA specs. You can find one near you at www.netaworld.org
You can also download the Acceptance Testing Specs (ATS) at that site that lists all the tests that should be performed.
RE: 11kV switchgear commissioning
Best Regards.
Slava
RE: 11kV switchgear commissioning
I actually looked for something like this.
a bit of my own research.
RE: 11kV switchgear commissioning
take 2
RE: 11kV switchgear commissioning
That's a pretty good document. Keep in mind, though, that much of the testing required for a good commissioning effort is going to be specialty equipment that requires trained personnel to operate and interpret results.
In the US, this usually means a specialty contractor as Zog and I and Slava have said.
old field guy
RE: 11kV switchgear commissioning
Again thank you
RE: 11kV switchgear commissioning
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: 11kV switchgear commissioning
Parts have also been left out, so it is incomplete, outdated, and for existing equipment. (Not to mention produced in violation of copyright laws)
RE: 11kV switchgear commissioning
I would actually take a moment to correct you.
the 2nd portion from this site
http://www.dymaxservice.com/case_studies.html
the first portion from
h
and
BN-SP-ES06 Inspection Procedure for Metal-Enclosed Medium/High Voltage Switchgear
There is a portion on the legal side for you as well
RE: 11kV switchgear commissioning
Again thank you for the advise zog zog
much appreciated.
Regards.
I dont understand why good standards is not freely available to the public to ensure safety and good practice for all.
RE: 11kV switchgear commissioning
Dymax should know better. I fyou look at the header of the document you posted you see MTS-2001? Thats NETA MTS 2001 version, dont worry, you didnt do anything wrong.
Where are you located?, perhaps I (Or OFG) can recommend a good testing group for you to call.
RE: 11kV switchgear commissioning
RE: 11kV switchgear commissioning